I thought about that, but I will still have to put sprinklers above due to the volume of the space within the beams being over 160 cuft., so that would end up adding more (above and below). Putting in a horizontal divider and the sheetrock panels would probably cost about as much installing the addition 12 sprinklers (18 vs. 6 if a flat ceiling), especially in this working condition. I ran the calc and the system would require 281 gpm. This translates to roughly a .45 density over the room. Looks like the sprinklers will end up being the way to go.

At 03:44 PM 12/26/2007, you wrote:
Hello Todd,

Cut the sheetrock to 2'8" or so to fit through the hatch on a diagonal. Use liquid nail to attach the sheetrock to the beams and Fire Caulk the beam to sheetrock joint. A 4'x8' sheet can be cut into 3 pieces 4' x 2'8" to reduce waste and make it easier to handle.

If the edge to edge of the beam flanges is not more that 24" it should not be any different to the sheetrock than on ceiling joist of 24" centers.


You should even be able to fill the space with Blown In Insulation if needed


Let me try some art work
        _____                   _____
          |                               |
          |                               |
          |                               |
          |                               |
          | ____sheetrock___ |
        -----o              o-----

        C = Metal Stud
        o = Fire Caulk


Wednesday, December 26, 2007, 1:35:18 PM, you wrote:

> I can't think of a good way to hold insulation at the top the beam.
> You might be able to do it with a spray on, but there is none on the
> job and the expense wouldn't be justified. I did a calculation and we
> couldn't even install a ceiling to get away from it because the
> volume of space between the two beams is 172 cuft, exceeding the 160
> cuft in the concealed space section. Sounds like we're screwed.


> At 12:00 PM 12/26/2007, you wrote:
>>bulls-eye

>>I guess one could simply use those bowed wire every couple of feet
>>(like one uses for insulation under the flooring in a house) but I
>>wouldn't be comfortable with that. What are you guys typically using
>>to reliable hold the insulation up?

>>Roland

>>On Dec 26, 2007, at 8:06 AM, Dewayne Martinez wrote:

>>>Todd,
>>>I think we talked somewhat about this in prior postings that the 22"
>>>deflector distance couldn't be modified so one of the ideas was to
>>>have
>>>non-combustible insulation installed at the deck to make the deflector
>>>to now within the 22" limit.  Now keeping the insulation up in the
>>>pockets bring about another problem.
>>>Dewayne

>>>-----Original Message-----
>>>From: [EMAIL PROTECTED]
>>>[mailto:[EMAIL PROTECTED] On Behalf Of Todd
>>>Williams - FPDC
>>>Sent: Wednesday, December 26, 2007 9:56 AM
>>>To: [email protected]
>>>Subject: Re: construction type - extra heads

>>>I have 30" deep beams spaced at 2'-9" o.c. If I space sprinklers in
>>>every pocket, I have 18 sprinklers protecting a 625 sqft unoccupied
>>>room. I was trying to look for a way out of it, since it does seem
>>>excessive and will have a monstrous effect on the calcs. The space is
>>>only accessible by a 2' x 2' hatch with a ladder, so bringing up
>>>sheetrock to cover the ceiling is not practical. Looking for
>>>thoughts or
>>>ideas.


>>>At 10:37 AM 12/26/2007, you wrote:
>>>>did you start with the definitions?  How can you call it anything but
>>>>obstructed?  I ASSUME the TC put the 3 to 7-1/2 ft since beam and
>>>>girders assemblies are TYPICALLY  spaced at a minimum but structural
>>>>loads are not always typical so neither are the beam placements.
>>>>Don't let the general description in the ANNEX get in the way of
>>>>defining ceiling type since it does NOT conflict with the base
>>>>definition.   Considering wood joists have the same impact on heat
>>>>flow and discharge, where's the beef?

>>>>The only time the minimum spacing will cause a REAL problem is
>>>>exceeding the 22 inch below the ceiling with concrete tees that are
>>>>less than 3 ft apart.  Twin tees are pretty common.

>>>>Roland

>>>>On Dec 24, 2007, at 5:38 AM, Todd Williams - FPDC wrote:

>>>>>I am working on room that is approximately 25 x 25. The roof deck is
>>>>>two layers of 3" thick tongue-and-grooved plank. Supporting this
>>>>>is a
>>>>>series of 30" deep steel beams spaced 2'-9" O.C. This room is
>>>>>presently unoccupied and will remain that way. (The space above was
>>>>>contained a water tank. This is in a tower of an old mill). In my
>>>>>pre-Christmas reading of the construction types, this seems to be an
>>>>>anomaly. How do you address construction where the beam spacing is
>>>>>less than 3 feet? Obstructed Construction only includes beams spaced
>>>>>between 3 and 7.5 feet.

>>>>>If you go to Chapter 8, assume obstructed construction and look
>>>>>at the

>>>>>deflector distances, I would have to include a sprinkler in each bay
>>>>>(since my beam depth exceeds 22"). I know I shouldn't be applying
>>>>>logic to sprinklers, but 18 sprinklers to protect a 25 x
>>>>>25 unoccupied room does seem to be overkill. Any thoughts? I think
>>>>>they are way over budget on this project, so the idea of adding a
>>>>>ceiling will be met with resistance. Any thoughts?

>>>>>Merry Christmas to all

>>>>>Todd G. Williams, PE
>>>>>Fire Protection Design/Consulting
>>>>>Stonington, Connecticut
>>>>>www.fpdc.com
>>>>>860.535.2080  _______________________________________________
>>>>>Sprinklerforum mailing list
>>>>>[email protected]
>>>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>>>>>To Unsubscribe, send an email to:Sprinklerforum-
>>>>>[EMAIL PROTECTED] (Put the word unsubscribe in the subject
>>>>>field)

>>>>_______________________________________________
>>>>Sprinklerforum mailing list
>>>>[email protected]
>>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>>>>To Unsubscribe, send an email
>>>>to:[EMAIL PROTECTED]
>>>>(Put the word unsubscribe in the subject field)

>>>Todd G. Williams, PE
>>>Fire Protection Design/Consulting
>>>Stonington, Connecticut
>>>www.fpdc.com
>>>860.535.2080
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>>>To Unsubscribe, send an email
>>>to:[EMAIL PROTECTED]
>>>(Put the word unsubscribe in the subject field)
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>>>To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
>>>(Put the word unsubscribe in the subject field)

>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>>(Put the word unsubscribe in the subject field)

> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)



--
Best regards,
Charles Thurston
 Coastal                            mailto:[EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to