did you start with the definitions? How can you call it anything but obstructed? I ASSUME the TC put the 3 to 7-1/2 ft since beam and girders assemblies are TYPICALLY spaced at a minimum but structural loads are not always typical so neither are the beam placements. Don't let the general description in the ANNEX get in the way of defining ceiling type since it does NOT conflict with the base definition. Considering wood joists have the same impact on heat flow and discharge, where's the beef?

The only time the minimum spacing will cause a REAL problem is exceeding the 22 inch below the ceiling with concrete tees that are less than 3 ft apart. Twin tees are pretty common.

Roland

On Dec 24, 2007, at 5:38 AM, Todd Williams - FPDC wrote:

I am working on room that is approximately 25 x 25. The roof deck is two layers of 3" thick tongue-and-grooved plank. Supporting this is a series of 30" deep steel beams spaced 2'-9" O.C. This room is presently unoccupied and will remain that way. (The space above was contained a water tank. This is in a tower of an old mill). In my pre-Christmas reading of the construction types, this seems to be an anomaly. How do you address construction where the beam spacing is less than 3 feet? Obstructed Construction only includes beams spaced between 3 and 7.5 feet.

If you go to Chapter 8, assume obstructed construction and look at the deflector distances, I would have to include a sprinkler in each bay (since my beam depth exceeds 22"). I know I shouldn't be applying logic to sprinklers, but 18 sprinklers to protect a 25 x 25 unoccupied room does seem to be overkill. Any thoughts? I think they are way over budget on this project, so the idea of adding a ceiling will be met with resistance. Any thoughts?

Merry Christmas to all

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to