I will have to check that out, maybe they have an online index or
something. I was dubious about using only one sidewall residential head with
a ceiling fan less than 8' away, and I still am.


Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Wednesday, January 30, 2008 4:27 PM
To: [email protected]
Subject: Re: 13 residential obstructions

There was also an article in FPC mag. and I believe it was also in sprinkler
age on the effect of ceiling fans on water distribution.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Bill Minkel" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, January 30, 2008 2:13 PM
Subject: RE: 13 residential obstructions


> In the same situation with a fan less than 8' from walls I was 
> instructed to use only one head per 2002 8.10.7.2.1.3, the four times 
> rule I think, since the residential sidewall could sprinkle both 
> sides, above and below, of the fan obstruction. So I did what I was told.
>
> Bill Minkel, Designer
> Western States Fire Protection, Dallas NFPA Member #2578666
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ed 
> Kramer
> Sent: Tuesday, January 29, 2008 3:32 PM
> To: [email protected]
> Subject: RE: 13 residential obstructions
>
> This thread reminds me of a dilemma I tussled with last week.  In 
> regards to residential sidewalls, section 8.10.7.1.2 (02) says not to 
> install residential sidewalls within 8' of a light "or similar 
> obstructions."  It doesn't provide any exceptions, such as the light 
> being only 4" deep and the sidewall installed 6" down from the 
> ceiling.  It simply says you can't do it.
>
> Is a soffit along the wall opposite the sidewall considered a "similar 
> obstruction"?  I have a project where a 24" deep soffit is installed 
> along
> 1
> wall of the bedroom and along 1 wall of the living area (for ductwork).
> Disregarding the soffits, sidewalls would work wonderfully.  If I 
> consider the soffit a "similar obstruction", that pretty much 
> eliminates the use of sidewalls.  Am I missing something?  Am I 
> misinterpreting the intent of 8.10.7.1.2?
>
> Ed Kramer
> Littleton, CO
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to