Consider low pressure DPVs if you have no way to determine trip time
(the expensive program). low pressure DPVs work on about a 30:1
differential rather than the more typical 6:1.

On Feb 1, 2008 7:06 AM, George Church <[EMAIL PROTECTED]> wrote:
> Is there a code requirement to provide hose valves in a parking garage in a
> 2-story?
>
> Would it make sense to toss em in the stairs and connect only to an FDC to
> effect a dry standpipe ?
>
> FDT water delivery would answer your question on how long it will take to
> trip/fill/and spurt water outa the ITC. If you depend on slapping an
> accelerator on after you flunk your first time trial, you may find out that
> its not enough and it's a little late and a lot expensive to slap in that
> other DPV, bulk, re-calc, resubmit, watch 30 days of calendar time elapse,
> and meet the opening date.
>
> We always toss in a low air supervisory switch and use tank-mounted air
> supplies. Even if they don't bother to hook up the switch, it was there and
> (in court) you can point out that you made heroic efforts to save them from
> themselves but they didn't take advantage of them, so your property carrier
> doesn't have to pay to thaw out/replace the dry system after a false trip,
> fire, whatever. After all, they'd have had plenty of time to respond to the
> warning if they'd bothered to hook it up, and this whole thing wouldn't have
> happened- so the fault rests on the Owner or someone other than yourself.
>
> As Ken points out to me, "You pay me a lot of money to observe 'Yeah,
> that'll sound good in court'" when I stray from a good decision.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
> [EMAIL PROTECTED]
> Sent: Friday, February 01, 2008 9:52 AM
> To: [email protected]
> Subject: RE: Parking Garage Sprinkler System ***
>
>
> Depending on where your riser is in relation to the remote part of your
> system you may have to have multiple systems to deal with the time
> factor.  It's a bit hard to determine without actually seeing everything
> you're seeing.
>
> Make the electrical guy move his lights, tell him fire protection is
> more critical.  Maybe he will move, maybe you will have to work around
> him.
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.lg.com
>
> at the outlet of most remote 1 1/2 in. hose stations should be
> 65 psi for hydraulically designed systems, so I think my fire pump head
> should be at least 80 psi? What do you think about this fire pump head,
> do you think it is low, high or good?
> ANSWER: That can only be answered once you've performed your
> calculations. Start there and make adjustments accordingly but depending
> on the configuration of the system, that might be close or a bit low to
> start with. Another thing to consider is will your fire department use
> the 1 1/2" fire hoses or will they want to bring their own hoses. If
> they prefer to provide their own, will they be 1 1/2" or
> 2 1/2" hoses? Here in the States we don't usually provide hoses since
> most people would hurt themselves trying to act like a fireman. We
> usually provide hose connections for the fire department to use. It is a
> matter of whether you intend to have these hoses handled by non-fire
> fighters or professional fire fighters. Plus hoses left in places like
> this
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to