Thanks to all for helping me with my question, according to your valuable 
comments I concluded that I should try the followings:
   
  I think an option is talking to a well known sprinkler manufacture to see if 
they can offer an extended coverage sprinkler suitable for my application, 
which can reduce my piping volume about 650 gallons in each story to be able to 
use one dry pipe system for each story. FDT seems to be a good program 
necessary for all fire sprinkler system designers, I should buy in near future.
   
  I think I sould better not to connect the fire hoses to sprinkler piping & 
should better design a dry standpipe system connecting to FDC, in this way I am 
not forced to choose a big pump to supply 65 psi at the outlet of 1 1/2 in. 
hose stations and I should only choose a pump to supply pressure demand of my 
sprinkler system.
   