How accurate is the FDT program based on comparison to field tests?
At 11:27 AM 2/1/2008, you wrote:
Reza:
As Ron points out the FDT program is expensive, but you may actually
save the cost of the program in this one installation if you can
reduce from 4 dry systems to just 2. We all need tools to do what we
do and FDT is just another tool.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Ron Greenman" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, February 01, 2008 8:35 AM
Subject: Re: Parking Garage Sprinkler System ***
Consider low pressure DPVs if you have no way to determine trip time
(the expensive program). low pressure DPVs work on about a 30:1
differential rather than the more typical 6:1.
On Feb 1, 2008 7:06 AM, George Church <[EMAIL PROTECTED]> wrote:
Is there a code requirement to provide hose valves in a parking garage in a
2-story?
Would it make sense to toss em in the stairs and connect only to an FDC to
effect a dry standpipe ?
FDT water delivery would answer your question on how long it will take to
trip/fill/and spurt water outa the ITC. If you depend on slapping an
accelerator on after you flunk your first time trial, you may find out that
its not enough and it's a little late and a lot expensive to slap in that
other DPV, bulk, re-calc, resubmit, watch 30 days of calendar time elapse,
and meet the opening date.
We always toss in a low air supervisory switch and use tank-mounted air
supplies. Even if they don't bother to hook up the switch, it was there and
(in court) you can point out that you made heroic efforts to save them from
themselves but they didn't take advantage of them, so your property carrier
doesn't have to pay to thaw out/replace the dry system after a false trip,
fire, whatever. After all, they'd have had plenty of time to respond to the
warning if they'd bothered to hook it up, and this whole thing wouldn't have
happened- so the fault rests on the Owner or someone other than yourself.
As Ken points out to me, "You pay me a lot of money to observe 'Yeah,
that'll sound good in court'" when I stray from a good decision.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, February 01, 2008 9:52 AM
To: [email protected]
Subject: RE: Parking Garage Sprinkler System ***
Depending on where your riser is in relation to the remote part of your
system you may have to have multiple systems to deal with the time
factor. It's a bit hard to determine without actually seeing everything
you're seeing.
Make the electrical guy move his lights, tell him fire protection is
more critical. Maybe he will move, maybe you will have to work around
him.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
at the outlet of most remote 1 1/2 in. hose stations should be
65 psi for hydraulically designed systems, so I think my fire pump head
should be at least 80 psi? What do you think about this fire pump head,
do you think it is low, high or good?
ANSWER: That can only be answered once you've performed your
calculations. Start there and make adjustments accordingly but depending
on the configuration of the system, that might be close or a bit low to
start with. Another thing to consider is will your fire department use
the 1 1/2" fire hoses or will they want to bring their own hoses. If
they prefer to provide their own, will they be 1 1/2" or
2 1/2" hoses? Here in the States we don't usually provide hoses since
most people would hurt themselves trying to act like a fireman. We
usually provide hose connections for the fire department to use. It is a
matter of whether you intend to have these hoses handled by non-fire
fighters or professional fire fighters. Plus hoses left in places like
this
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080