the building code says: ..sprinkler systems shall be installed throughout in accordance with NFPA 13. That means the areas that are allowed omission of sprinklers still provides protection throughout.

It says the same thing on 13R (for which many trade-ups are allowed) and the building is considered sprinklered throughout with the attic and concealed combustible spaces having no protection.


Roland

On Feb 14, 2008, at 11:19 AM, Randy Knutson wrote:

Forum Members,



When it says in the IFC (section 903.1.1 2003ed) to "Equip Throughout" with sprinkler system, does omitting sprinklers above ceilings in non- combustible
construction (per NFPA  13:8.14.1.2.2 2002ed) make it not "equipped
throughout"?

I have an I-3 occupancy in a Type 1 B building. The inspector says I need
sprinklers above the ceiling. Are they really required there?



Thanks for any help.



Randy Knutson

Shilo Automatic Sprinkler, Inc.