the building code says: ..sprinkler systems shall be installed
throughout in accordance with NFPA 13.
That means the areas that are allowed omission of sprinklers still
provides protection throughout.
It says the same thing on 13R (for which many trade-ups are allowed)
and the building is considered sprinklered throughout with the attic
and concealed combustible spaces having no protection.
Roland
On Feb 14, 2008, at 11:19 AM, Randy Knutson wrote:
Forum Members,
When it says in the IFC (section 903.1.1 2003ed) to "Equip
Throughout" with
sprinkler system, does omitting sprinklers above ceilings in non-
combustible
construction (per NFPA 13:8.14.1.2.2 2002ed) make it not "equipped
throughout"?
I have an I-3 occupancy in a Type 1 B building. The inspector says
I need
sprinklers above the ceiling. Are they really required there?
Thanks for any help.
Randy Knutson
Shilo Automatic Sprinkler, Inc.