It is ok not to have the 10d if the suction pipe go from vertical to
horizontal. However if a horizontal line change into 90 deg. horizontally
you can overload one side of the impeller and potentially have some
vibration etc... problems.
Peter Nadhazy Cell (508)493-3933
Marathon Fire Protection, Inc.
578 Arcade Avenue
PO BOX 160
Seekonk, MA 02771
(508)336-4300
Fax :(508)336-4232
email: [EMAIL PROTECTED]
www.marathonfire.com
----- Original Message -----
From: "Jamie Seidl" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, February 15, 2008 11:21 AM
Subject: Vertical Inline
Forum,
We are having a discussion in our office about pumps. I have always thought
that a vertical in-line pump didn't need to have the 10 pipe diameter
distance on the suction side since 5.14.6.3.1, 5.14.6.3.2, and 5.14.6.3.3
all reference "horizontal split case pumps.
Have I missed something?