Except that it took an IBC Code cycle to attain this "fully sprinklered" status for #13R, I believe 2000 ->2003.
glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Thursday, February 14, 2008 2:44 PM To: [email protected] Subject: Re: Fully Sprinklered Definition the building code says: ..sprinkler systems shall be installed throughout in accordance with NFPA 13. That means the areas that are allowed omission of sprinklers still provides protection throughout. It says the same thing on 13R (for which many trade-ups are allowed) and the building is considered sprinklered throughout with the attic and concealed combustible spaces having no protection. Roland On Feb 14, 2008, at 11:19 AM, Randy Knutson wrote: > Forum Members, > > > > When it says in the IFC (section 903.1.1 2003ed) to "Equip > Throughout" with > sprinkler system, does omitting sprinklers above ceilings in non- > combustible > construction (per NFPA 13:8.14.1.2.2 2002ed) make it not "equipped > throughout"? > > I have an I-3 occupancy in a Type 1 B building. The inspector says > I need > sprinklers above the ceiling. Are they really required there? > > > > Thanks for any help. > > > > Randy Knutson > > Shilo Automatic Sprinkler, Inc. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)