I agree with Art.  A horizontal split case pump takes suction from both
sides of the impeller, so non-laminar flow can mess with it.  Thus the
requirements of the sections you mention.  An inline pump takes suction from
only one side of the impeller.  Non-laminar flow isn't a critical issue and
those sections only reference horizontal split case pumps.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Jamie Seidl
> Sent: Friday, February 15, 2008 9:22 AM
> To: [email protected]
> Subject: Vertical Inline
> 
> Forum,
> We are having a discussion in our office about pumps. I have always
> thought that a vertical in-line pump didn't need to have the 10 pipe
> diameter distance on the suction side since 5.14.6.3.1, 5.14.6.3.2, and
> 5.14.6.3.3 all reference "horizontal split case pumps.
> 
> Have I missed something?
> 