This is a repeat, as my previous e-mail somehow never got posted. A building is being used for manufacuring Glass fiber reinforced resin products. (I think the products are bath tubs etc., but not sure yet). Some material used, such as Polyester Resins, Methyl Ethyl Ketone Peroxyde (MEKP), Acetone etc. are class 1C flammable liquids.
The owner states that "Polyester resins will be stored in resin rooms. Acetone in certified containers throughout shop space. And MEKP catalysts will be stored in certified containers at workstations. Also, composite plastic molds will be stored on racks, 5 to 12 feet high." The engineer of record has specified OH2 for the building and when questioned is directing to NFPA 33, 2000, section 15.3. I think the storage areas have to be designed as per NFPA 30 for flammable liquids, and as per NFPA 13 for plastic storage. Will the storage quantities be a deciding factor (for selecting OH2)? Will the process areas and spray application areas be OH2 (as per NFPA 33)? Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)