Hello Todd, No room in the existing building for a pump room. Suction will be coming from a city supply line now. THEN we get to run a 6 inch supply line 500 feet across the building and half way down the building to the existing riser manifold. They were going to put in a "Full Load" generator when this started but that has gone away now.
Friday, February 15, 2008, 2:07:39 PM, you wrote: > In general, I would say diesel as well, but each situation is > different. If this is a retrofit, look at the installation issues. It > may be better to install a pump inside the existing building and put > a generator outside as opposed to a new building/addition to house > the diesel. Where are they going to be getting the suction water from? > At 07:32 AM 2/15/2008, you wrote: >>Hello sprinklerforum, >> >> I am looking for opinions on installing a Diesel fire pump Vs installing >> an Electric fire pump and Gen Set. I have a location that is being >> cut loose from the "Site Wide" fire pump loop now owned by others. >> >>-- >>Best regards, >> Charles mailto:[EMAIL PROTECTED] >>Coastal Fire Protection >> >>_______________________________________________ >>Sprinklerforum mailing list >>[email protected] >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >>To Unsubscribe, send an email to:[EMAIL PROTECTED] >>(Put the word unsubscribe in the subject field) > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, Connecticut > www.fpdc.com > 860.535.2080 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) -- Best regards, Charles mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)