NFPA 20 says nothing about testing of generators. NFPA 72 says the following:
4.4.1.9.4 Performance, Operation, Testing, and Maintenance. The requirements for performance, operation, testing, and maintenance of engine-driven generators shall conform to the applicable provisions of NFPA 110, Standard for Emergency and Standby Power Systems. 4.4.7.3.1.4 Monitoring shall not be required for the output of an engine-driven generator that is part of the secondary power supply, provided the generator is tested weekly in accordance with Chapter 10. 8.3.5.2.2 The subsidiary facility shall be inspected at least monthly by central station personnel for the purpose of verifying the operation of all supervised equipment, all telephones, all battery conditions, and all fluid levels of batteries and generators. (refers to Central Station only) Table 10.4.2.2 Test Methods: If an engine-driven generator dedicated to the fire alarm system is used as a required power source, operation of the generator shall be verified in accordance with NFPA 110, Standard for Emergency and Standby Power Systems, by the building owner. There are some other references to generator testing as to frequencies when connected to a FACP but nothing about pumps. (I didn't expect to find anything in 20 or 72 as these are not the appropriate documents.) Here is what NFPA 110 says: Chapter 8 Routine Maintenance and Operational Testing 8.1* General. 8.1.1 The routine maintenance and operational testing program shall be based on all of the following: (1) Manufacturer's recommendations (2) Instruction manuals (3) Minimum requirements of this chapter (4) The authority having jurisdiction 8.1.2 Consideration shall be given to temporarily providing a portable or alternate source whenever the emergency generator is out of service. 8.2* Manuals, Special Tools, and Spare Parts. 8.2.1 At least two sets of instruction manuals for all major components of the EPSS shall be supplied by the manufacturer(s) of the EPSS and shall contain the following: (1) A detailed explanation of the operation of the system (2) Instructions for routine maintenance (3) Detailed instructions for repair of the EPS and other major components of the EPSS (4) An illustrated parts list and part numbers (5) Illustrated and schematic drawings of electrical wiring systems, including operating and safety devices, control panels, instrumentation, and annunciators 8.2.2 For Level 1 systems, instruction manuals shall be kept in a secure, convenient location, one set near the equipment, and the other set in a separate location. 8.2.3 Special tools and testing devices necessary for routine maintenance shall be available for use when needed. 8.2.4 Replacement for parts identified by experience as high mortality items shall be maintained in a secure location(s) on the premises. 8.2.4.1 Consideration shall be given to stocking spare parts as recommended by the manufacturer. 8.3 Maintenance and Operational Testing. 8.3.1* The EPSS shall be maintained to ensure to a reasonable degree that the system is capable of supplying service within the time specified for the type and for the time duration specified for the class. 8.3.2 A routine maintenance and operational testing program shall be initiated immediately after the EPSS has passed acceptance tests or after completion of repairs that impact the operational reliability of the system. 8.3.2.1 The operational test shall be initiated at an automatic transfer switch and shall include testing of each EPSS component on which maintenance or repair has been performed, including the transfer of each automatic and manual transfer switch to the alternate power source, for a period of not less than 30 minutes under operating temperature. 8.3.3 A written schedule for routine maintenance and operational testing of the EPSS shall be established. 8.3.4 A permanent record of the EPSS inspections, tests, exercising, operation, and repairs shall be maintained and readily available. 8.3.4.1 The permanent record shall include the following: (1) The date of the maintenance report (2) Identification of the servicing personnel (3) Notation of any unsatisfactory condition and the corrective action taken, including parts replaced (4) Testing of any repair for the time as recommended by the manufacturer 8.3.5* Transfer switches shall be subjected to a maintenance and testing program that includes all of the following operations: (1) Checking of connections (2) Inspection or testing for evidence of overheating and excessive contact erosion (3) Removal of dust and dirt (4) Replacement of contacts when required 8.3.6 Paralleling gear shall be subject to inspection, testing, and maintenance program that includes all of the following operations: (1) Checking of connections (2) Inspection or testing for evidence of overheating and excessive contact erosion (3) Removal of dust and dirt (4) Replacement of contacts when required 8.3.7* Storage batteries, including electrolyte levels or battery voltage, used in connection with systems shall be inspected weekly and maintained in full compliance with manufacturer's specifications. 8.3.7.1 Maintenance of lead-acid batteries shall include the monthly testing and recording of electrolyte specific gravity. Battery conductance testing shall be permitted in lieu of the testing of specific gravity when applicable or warranted. 8.3.7.2 Defective batteries shall be replaced immediately upon discovery of defects. 8.3.8 A fuel quality test shall be performed at least annually using tests approved by ASTM standards. 8.4 Operational Inspection and Testing. 8.4.1* EPSSs, including all appurtenant components, shall be inspected weekly and exercised under load at least monthly. 8.4.1.1 If the generator set is used for standby power or for peak load shaving, such use shall be recorded and shall be permitted to be substituted for scheduled operations and testing of the generator set, providing the same record as required by 8.3.4. 8.4.2* Diesel generator sets in service shall be exercised at least once monthly, for a minimum of 30 minutes, using one of the following methods: (1) Loading that maintains the minimum exhaust gas temperatures as recommended by the manufacturer. (2) Under operating temperature conditions and at not less than 30 percent of the EPS nameplate kW rating. (3) If the engine cannot be loaded as required in (2), the engine shall be operated until the water temperature and the oil pressure have stabilized and then the test shall be terminated before the 30 minute time period expires. 8.4.2.1 The date and time of day for required testing shall be decided by the owner, based on facility operations. 8.4.2.2 Equivalent loads used for testing shall be automatically replaced with the emergency loads in case of failure of the primary source. 8.4.2.3* Diesel-powered EPS installations that do not meet the requirements of 8.4.2 shall be exercised monthly with the available EPSS load and exercised annually with supplemental loads at 25 percent of nameplate rating for 30 minutes, followed by 50 percent of nameplate rating for 30 minutes, followed by 75 percent of nameplate rating for 60 minutes, for a total of 2 continuous hours. 8.4.2.4 Spark-ignited generator sets in service shall be exercised at least once monthly, for a minimum of 30 minutes, using one of the following methods: (1) Loading that maintains the minimum exhaust gas temperatures as recommended by the manufacturer (2) Under operating temperature conditions and at not less than 30 percent of the EPS nameplate kW rating 8.4.2.4.1 The date and time of day for required testing shall be decided by the owner, based on facility operations. 8.4.2.4.2 Equivalent loads used for testing shall be automatically replaced with the emergency loads in case of failure of the primary source. 8.4.3 The EPS test can be initiated by simulating a power outage using the test switch(es) on the ATSs or by opening a normal breaker. Opening a normal breaker shall not be required. 8.4.4 Load tests of generator sets shall include complete cold starts. 8.4.5 Time delays shall be set as follows: (1) Time delay on start: (a) 1 second minimum (b) 0.5 second minimum for gas turbine units (2) Time delay on transfer to emergency: no minimum required (3) Time delay on restoration to normal: 5 minutes minimum (4) Time delay on shutdown: 5 minutes minimum 8.4.6 Transfer switches shall be operated monthly. 8.4.6.1 The monthly test of a transfer switch shall consist of electrically operating the transfer switch from the standard position to the alternate position and then a return to the standard position. 8.4.7* EPSS circuit breakers for Level 1 system usage, including main and feed breakers between the EPS and the transfer switch load terminals, shall be exercised annually with the EPS in the "off" position. 8.4.7.1 Circuit breakers rated in excess of 600 volts for Level 1 system usage shall be exercised every 6 months and shall be tested under simulated overload conditions every 2 years. 8.4.8 The routine maintenance and operational testing program shall be overseen by a properly instructed individual. 8.4.9* Level 1 EPSS shall be tested for the duration of its assigned class (see Section 4.2), for at least 4 hours, at least once within every 36 months. 8.4.9.1 The load shall be the EPSS system load running at the time of the test. The test shall be initiated by opening all switches or breakers supplying normal power to the EPSS. 8.4.9.2 A power interruption to non-EPSS loads shall not be required. Kind of wide open isn't it? Reminds me of the old 13A--"You ought to take care of this thing but it's your building so do as you wish." Since "this thing" in this case is hooked into the life safety/property protection portion of the building, and since we've pretty much established that those things, due to there stand-by nature and importance, need testing, and that a fire in your building effects my pocketbook (cost of fire services, impact to environment, down production time (no wealth being produced for the community but wealth being consumed in the form of unemployment benefits, increased rates for competitive products due to shortage of supply without change in demand, etc.), and increased across the board insurance rates (yes, we all get to pay a little extra every time insurance companies spend money), then we should have a say in how these devices are maintained and we do that through regulation. Soapbox put away and don't show that sentence to my English teacher. On 2/16/08, danarbel <[EMAIL PROTECTED]> wrote: > Regarding the Generator, I'm looking for requirements in NFPA 20, 110, 72 > regarding the same supervisory requirements as applied to the Diesel Pump in > NFPA 20. > > Dan > > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins > Sent: 16 February, 2008 5:17 PM > To: [email protected] > Subject: Re: Diesel vs Electric > > FM undertook a reliability study about 10 years ago, based on results of > pump tests during inspections and loss information. The results were > interesting in that the electric pumps were more reliable when tested, > but were much more likely to fail during a fire due to power loss > resulting from the fire or "pulling the plug" on the main supply for > safety sake. The net result was that diesel pumps are more reliable > overall, but only so long as they are properly tested and maintained. > > As regards diesel/generator sets, it turns out that the weak link is the > transfer switch. The transfer switch can not only fail to operate when > power is lost, but also can fail when there is no power loss, preventing > the pump from running. The net result is that the electric pump with > diesel backup is probably less reliable than either an electric pump or > a diesel pump alone. It certainly isn't worth the large extra expense in > terms of reliability. > > Joe > > Charles Thurston wrote: > > Hello sprinklerforum, > > > > I am looking for opinions on installing a Diesel fire pump Vs installing > > an Electric fire pump and Gen Set. I have a location that is being > > cut loose from the "Site Wide" fire pump loop now owned by others. > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > No virus found in this incoming message. > Checked by AVG Free Edition. > Version: 7.5.516 / Virus Database: 269.20.6/1282 - Release Date: 15-Feb-08 > 7:08 PM > > > No virus found in this outgoing message. > Checked by AVG Free Edition. > Version: 7.5.516 / Virus Database: 269.20.6/1282 - Release Date: 15-Feb-08 > 7:08 PM > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)