Joe, I'm being a Chatty Cathy today but you just confirmed my anecdotal experience with pumps, generators and transfer switches. Although I'm sure I haven't had as much experience as many others on this list I have touched my fair share. I might add from my straw poll experience that neglected diesels seem to rapidly deteriorate whereas the electric drivers and controllers are pretty reliable even after long periods of neglect. Of course the pumps themselves don't take kindly to neglect but reliability issues are equal regardless of drivers. Another generator/transfer switch problem, which harkens back to an earlier today post on the alarm forum by John Drucker, is who does the maintenance? I can think of at least one fire where the transfer switch worked but the generator failed to start because there wasn't any fuel. I can also point to that problem during testing and another with the transfer switch failure, and another where the batteries to generator weren't connected and another where a relay in the starter circuit failed. In all cases the company was there for a full IT&M of all fire protection equipment but how often is the entire building fire protection treated as an integrated system once it's been commissioned? often the interfaces are ignored due to speciality of trades and the lack of a knowledgeable life safety coordinator. But that's a different topic.
On Feb 16, 2008 7:17 AM, Joe Hankins <[EMAIL PROTECTED]> wrote: > FM undertook a reliability study about 10 years ago, based on results of > pump tests during inspections and loss information. The results were > interesting in that the electric pumps were more reliable when tested, > but were much more likely to fail during a fire due to power loss > resulting from the fire or "pulling the plug" on the main supply for > safety sake. The net result was that diesel pumps are more reliable > overall, but only so long as they are properly tested and maintained. > > As regards diesel/generator sets, it turns out that the weak link is the > transfer switch. The transfer switch can not only fail to operate when > power is lost, but also can fail when there is no power loss, preventing > the pump from running. The net result is that the electric pump with > diesel backup is probably less reliable than either an electric pump or > a diesel pump alone. It certainly isn't worth the large extra expense in > terms of reliability. > > Joe > > Charles Thurston wrote: > > Hello sprinklerforum, > > > > I am looking for opinions on installing a Diesel fire pump Vs installing > > an Electric fire pump and Gen Set. I have a location that is being > > cut loose from the "Site Wide" fire pump loop now owned by others. > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)