Regarding the Generator, I'm looking for requirements in NFPA 20, 110, 72
regarding the same supervisory requirements as applied to the Diesel Pump in
NFPA 20.

Dan



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins
Sent: 16 February, 2008 5:17 PM
To: [email protected]
Subject: Re: Diesel vs Electric

FM undertook a reliability study about 10 years ago, based on results of 
pump tests during inspections and loss information. The results were 
interesting in that the electric pumps were more reliable when tested, 
but were much more likely to fail during a fire due to power loss 
resulting from the fire or "pulling the plug" on the main supply for 
safety sake. The net result was that diesel pumps are more reliable 
overall, but only so long as they are properly tested and maintained.

As regards diesel/generator sets, it turns out that the weak link is the 
transfer switch. The transfer switch can not only fail to operate when 
power is lost, but also can fail when there is no power loss, preventing 
the pump from running. The net result is that the electric pump with 
diesel backup is probably less reliable than either an electric pump or 
a diesel pump alone. It certainly isn't worth the large extra expense in 
terms of reliability.

Joe

Charles Thurston wrote:
> Hello sprinklerforum,
>
>   I am looking for opinions on installing a Diesel fire pump Vs installing
>   an Electric fire pump and Gen Set. I have a location that is being
>   cut loose from the "Site Wide" fire pump loop now owned by others.
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.20.6/1282 - Release Date: 15-Feb-08
7:08 PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.20.6/1282 - Release Date: 15-Feb-08
7:08 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to