This should satisfy the water purveyor.
They have no jurisdiction past the backflow (RP ASSE 1013).
With a  swing check and 1/32 hole drilled in clapper, you have room  for 
expansion.
 
Forest
Cherokee Fire

-----Original Message-----
> From:  [EMAIL PROTECTED] [mailto:sprinklerforum-
>  [EMAIL PROTECTED] On Behalf Of Brian
> Sent: Tuesday, February  26, 2008 2:27 PM
> To: [email protected]
> Subject:  RP Backflow with Antifreeze Loop
> 
> Anyone see any problems with  this: Having a 4" RP Backflow at the base
> of riser and then tapping an  antifreeze system off of the wet system but
> instead of an expansion  chamber (as required by code for a double check)
> running the old style  a/f 5ft loop off of this. Reasoning is since an RP
> type backflow ports  when overpressurized on system side the a/f system
> can still expand  through the loop like in the good ol' days.
> 
> It seems NFPA#13  only requires the expansion chamber since it would be
> impossible for  the antifreeze to otherwise expand since everything is
> 'locked' in  place by the double check. However with an RP backflow it
> would allow  the backwards movement of water neccessary for expansion and
> the loop  would perform it's duties of acting as a container for the
> antifreeze  and not be ported out with the water.
> 
> We had this arrangement  ok'd by an AHJ in the past but want to see if
> there is something we're  overlooking.
> 
> thx,
> 
>  







**************Ideas to please picky eaters. Watch video on AOL Living.      
(http://living.aol.com/video/how-to-please-your-picky-eater/rachel-campos-duffy/
2050827?NCID=aolcmp00300000002598)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to