Ed:
In Colo you are under the Dept. of health for backflow prevention,
specifically the "Colorado Cross Connection Control Manual" This places the
requirements for cross connection control on the water purveyors, and allows
the use of double check valve assemblies for fire protection that don't
contain additive's. The water purveyor can require all backflows for FP to
be RPZ type, but the state does not.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Ed Kramer" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, February 27, 2008 7:55 AM
Subject: RE: RP BFP on ALL systems
Thanks, Craig. What edition of IPC is that from?
Ed Kramer
Littleton, CO
-----Original Message-----
From: [EMAIL PROTECTED] [mailto:sprinklerforum-
[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, February 27, 2008 7:17 AM
To: [email protected]
Subject: RE: RP BFP on ALL systems
IPC Table 608.1 refers to Double Check, Double Check detector, Reduced
Pressure, Reduced Pressure Detector styles applicable to fire
protection. Take your pick, but check with the water purveyor first as
they may have specific requirements that nail it down.
608.16.4 Says sprinkler systems are to use double-check valve assembly
or reduced pressure. Also some interesting exceptions for deluge,
preaction or dry systems.
RP's are the standard for chemical additive systems like antifreeze.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Tuesday, February 26, 2008 9:39 PM
To: [email protected]
Subject: RP BFP on ALL systems
John, thanks for that tidbit. We have a few jurisdictions in this area
that require the RP on all systems, but most don't. Being a sprinkler
guy, I really don't pay much attention to what edition of what plumbing
code is being enforced. I guess I need to rethink that. Can anyone
clue me in on what the International Plumbing Code says concerning
BFP's?
Ed Kramer
Littleton, CO
> The 2006 National Standard Plumbing Code provides the requirement for
> RPZ when antifreeze is present (type not stipulated) or an FDC is
> present (the 1700ft distance to non potable source has been
> eliminated) on a water based fire protection system.
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)