> Thanks, Craig.  What edition of IPC is that from?
>
> Ed Kramer
> Littleton, CO
>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
[mailto:sprinklerforum-
>> [EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
>> Sent: Wednesday, February 27, 2008 7:17 AM
>> To: [email protected]
>> Subject: RE: RP BFP on ALL systems
>>
>> IPC Table 608.1 refers to Double Check, Double Check detector,
Reduced
>> Pressure, Reduced Pressure Detector styles applicable to fire
>> protection.  Take your pick, but check with the water purveyor first
as
>> they may have specific requirements that nail it down.
>>
>> 608.16.4 Says sprinkler systems are to use double-check valve
assembly
>> or reduced pressure.  Also some interesting exceptions for deluge,
>> preaction or dry systems.
>>
>> RP's are the standard for chemical additive systems like antifreeze.
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection Group
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> [EMAIL PROTECTED]
>> http://www.lg.com
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Ed
Kramer
>> Sent: Tuesday, February 26, 2008 9:39 PM
>> To: [email protected]
>> Subject: RP BFP on ALL systems
>>
>> John, thanks for that tidbit.  We have a few jurisdictions in this
area
>> that require the RP on all systems, but most don't.  Being a
sprinkler
>> guy, I really don't pay much attention to what edition of what
plumbing
>> code is being enforced.  I guess I need to rethink that.  Can anyone
>> clue me in on what the International Plumbing Code says concerning
>> BFP's?
>>
>> Ed Kramer
>> Littleton, CO
>>
>>
>> > The 2006 National Standard Plumbing Code provides the requirement
for
>> > RPZ when antifreeze is present (type not stipulated) or an FDC is
>> > present (the 1700ft distance to non potable source has been
>> > eliminated) on a water based fire protection system.
>> >
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum-
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to