This is a 3 head design & yes that is the area that is failing....
Brian Harris FDFP INC. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Monday, April 07, 2008 4:16 PM To: [email protected] Subject: Re: Failed Bucket Test Brian: Are you a 4 head design or do you have areas of 13 to calc? A booster pump approved by the AHJ may be the cheapest alternative, if you have a lot of 13 area to deal with.(I'm assuming that the 4head residential calc is not where your short, if it is the 4 head area can you change the heads to ones with larger orifices?) I know that TALCO has a packaged 13R fire pump that conforms to NFPA 20 for up to 500 GPM Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Brian Harris" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Monday, April 07, 2008 1:05 PM Subject: RE: Failed Bucket Test > The city the job is in will not let anybody but the Fire Dept. run the > test. > > > > Brian Harris > FDFP INC. > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Jeff > Hewitt > Sent: Monday, April 07, 2008 3:02 PM > To: [email protected] > Subject: Re: Failed Bucket Test > > Brian, > > Just curious... > > What were the circumstances that led you to use a test conducted by > the Fire Department? Are there conservation limitations imposed or > something like that? Why would you not have performed your own test? > > Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer > Bi-State Fire Protection Corporation > 241 Hughes Lane > St. Charles, MO 63301 > 636-946-0011 > 636-946-5172 (FAX) > > This e-mail and any attachments are CONFIDENTIAL and may be protected > by one or more legal privileges. It is intended solely for the use of > the addressee identified above. If you are not the intended > recipient, any use, disclosure, copying or distribution of this e-mail > is unauthorized. If you received this e-mail in error, please notify > the sender immediately at the above captioned address. > ----- Original Message ----- > From: "Brian Harris" <[EMAIL PROTECTED]> > To: <[email protected]> > Sent: Monday, April 07, 2008 1:51 PM > Subject: RE: Failed Bucket Test > > >> Chuck, >> Yeah that was one of the first things we did, we also had the local >> Utility Dept. go out and check and they found nothing. >> >> >> Brian Harris >> FDFP INC. >> >> -----Original Message----- >> From: [EMAIL PROTECTED] >> [mailto:[EMAIL PROTECTED] On Behalf Of Chuck >> Bowman >> Sent: Monday, April 07, 2008 2:42 PM >> To: [email protected] >> Subject: RE: Failed Bucket Test >> >> Brian, >> Has anyone checked to make sure all the valves are fully open, just a >> suggestion. >> Chuck >> >> -----Original Message----- >> From: [EMAIL PROTECTED] >> [mailto:[EMAIL PROTECTED] On Behalf Of Brian >> Harris >> Sent: Monday, April 07, 2008 2:31 PM >> To: [email protected] >> Subject: Failed Bucket Test >> >> Fellow forum people: >> I have a situation where we have designed and installed a 13R system, >> it is completely finished and wham-o we fail the bucket test! Our >> system was designed based on the flow test provided by the city fire >> dept., turns out that a test taken now with the failed test shows a >> 25% drop in static & residual pressures, hence the failed test. Of >> course the owner is looking to us to pull a magic rabbit out of our >> #$% , err I mean hat, we have tried a few different things but with >> that big of a pressure loss there's really not much we can do. I >> don't feel it's our liability at this point since we went off the >> city's water flow test and per the calc's we were good, any thoughts? >> >> >> Regards, >> >> >> <http://www.firstdefensefire.com/> >> >> >> >> >> >> >> >> >> E-mail message checked by Spyware Doctor (5.5.0.178) Database version: >> 5.09560 http://www.pctools.com/spyware-doctor/ >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email >> to:[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) >> >> >> >> >> >> E-mail message checked by Spyware Doctor (5.5.0.178) Database version: >> 5.09560 http://www.pctools.com/spyware-doctor/ >> >> >> >> >> >> E-mail message checked by Spyware Doctor (5.5.0.178) Database >> version: 5.09560 http://www.pctools.com/spyware-doctor/ >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email >> to:[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > > > > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version: > 5.09560 http://www.pctools.com/spyware-doctor/ > > > > > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version: > 5.09560 http://www.pctools.com/spyware-doctor/ > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) E-mail message checked by Spyware Doctor (5.5.0.178) Database version: 5.09560 http://www.pctools.com/spyware-doctor/ E-mail message checked by Spyware Doctor (5.5.0.178) Database version: 5.09560 http://www.pctools.com/spyware-doctor/ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)