Brian,

Static doesn't change, even with a blockage (recovery time is slower
but eventually reaches the pre-recorded pressure--hence the value of a
main drain test), unless the original test was done during off-peak
and your bucket test was done during peak, there is a pump involved
that is not coming on or has been removed from service (your bucket
test may not have enough demand to fire it up but a hydrant test
would--this begs the differences in static), the grid has been changed
and the source, if gravity, is lower, relative to the site, than
before, the level of the tank was lower during your test (25 psi
equals a little less than 11 feet) or the guy that produced the
original numbers didn't know what he was doing (I got a report once
that showed the residual pressure and velocity pressure to be the
same--the water guy wouldn't budge). If you're in a residential area
I'd look at the time of day and time of year the test was done as well
as the area, read grid, growth since the time the test was done. Mid
day and mid night are off peak times as is winter in general during
peak. The tanks may be low and your test may have been done during or
at the end of morning peak or the beginning of evening peak. The
original test may have been done during summer at midnight when usage
was down and the tanks freshly replenished for tomorrow's lawn
watering. Lots of possibilities. I think our reliable, automatic water
supplies are less than reliable but the alternative seems to be stored
water and pumps--extra equipment to fail.

On Tue, Apr 8, 2008 at 7:22 AM, Brian Harris <[EMAIL PROTECTED]> wrote:
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to