25 psi equals 57.7 feet of elevation and partially closed valves can account for a reduced static pressure when dealing with city water mains.
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman Sent: Tuesday, April 08, 2008 8:32 AM To: [email protected] Subject: Re: Failed Bucket Test Brian, Static doesn't change, even with a blockage (recovery time is slower but eventually reaches the pre-recorded pressure--hence the value of a main drain test), unless the original test was done during off-peak and your bucket test was done during peak, there is a pump involved that is not coming on or has been removed from service (your bucket test may not have enough demand to fire it up but a hydrant test would--this begs the differences in static), the grid has been changed and the source, if gravity, is lower, relative to the site, than before, the level of the tank was lower during your test (25 psi equals a little less than 11 feet) or the guy that produced the original numbers didn't know what he was doing (I got a report once that showed the residual pressure and velocity pressure to be the same--the water guy wouldn't budge). If you're in a residential area I'd look at the time of day and time of year the test was done as well as the area, read grid, growth since the time the test was done. Mid day and mid night are off peak times as is winter in general during peak. The tanks may be low and your test may have been done during or at the end of morning peak or the beginning of evening peak. The original test may have been done during summer at midnight when usage was down and the tanks freshly replenished for tomorrow's lawn watering. Lots of possibilities. I think our reliable, automatic water supplies are less than reliable but the alternative seems to be stored water and pumps--extra equipment to fail. On Tue, Apr 8, 2008 at 7:22 AM, Brian Harris <[EMAIL PROTECTED]> wrote: > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)