Ron,
Duh!!!!!! I reckon I need to set the problem up right to get a good
answer. GIGO! Now that I've been corrected is a 58 foot difference in
tank level reasonable? 25 feet maybe I think.
On Apr 8, 2008, at 9:21 AM, Fletcher, Ron wrote:
Ron,
25 ft = 10.825 psi
25 psi = 57.7 feet
Ron
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Tuesday, April 08, 2008 9:13 AM
To: [email protected]
Subject: Re: Failed Bucket Test
Ron,
Check your math: 25.0 x 0.433 = 10.825
On Apr 8, 2008, at 8:47 AM, Fletcher, Ron wrote:
25 psi equals 57.7 feet of elevation and partially closed valves can
account for a reduced static pressure when dealing with city water
mains.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Tuesday, April 08, 2008 8:32 AM
To: [email protected]
Subject: Re: Failed Bucket Test
Brian,
Static doesn't change, even with a blockage (recovery time is slower
but eventually reaches the pre-recorded pressure--hence the value
of a
main drain test), unless the original test was done during off-peak
and your bucket test was done during peak, there is a pump involved
that is not coming on or has been removed from service (your bucket
test may not have enough demand to fire it up but a hydrant test
would--this begs the differences in static), the grid has been
changed
and the source, if gravity, is lower, relative to the site, than
before, the level of the tank was lower during your test (25 psi
equals a little less than 11
feet) or the guy that produced the original numbers didn't know what
he was doing (I got a report once that showed the residual pressure
and velocity pressure to be the same--the water guy wouldn't budge).
If you're in a residential area I'd look at the time of day and time
of year the test was done as well as the area, read grid, growth
since
the time the test was done. Mid day and mid night are off peak times
as is winter in general during peak. The tanks may be low and your
test may have been done during or at the end of morning peak or the
beginning of evening peak. The original test may have been done
during
summer at midnight when usage was down and the tanks freshly
replenished for tomorrow's lawn watering. Lots of possibilities. I
think our reliable, automatic water supplies are less than reliable
but the alternative seems to be stored water and pumps--extra
equipment to fail.
On Tue, Apr 8, 2008 at 7:22 AM, Brian Harris
<[EMAIL PROTECTED]> wrote:
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Ron Greenman
...at home
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Ron Greenman
...at home
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)