Forum members - your opinions on the following situation, please:
Design standard is 13R 2007 edition. System type will be antifreeze with a volume exceeding 40 gallon. Per 13R section 6.8.4, "Piping shall be sized using hydraulic calculation procedures in accordance with NFPA 13". NFPA 13 says to use the Darcy-Weisbach method (section 22.4.4.5.1). Do you think it's the intent of 13R to require the calcs be done using Darcy-Weisbach? Ed Kramer Littleton, CO _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)