On Thu, Apr 17, 2008 at 2:59 PM, Ed Kramer <[EMAIL PROTECTED]> wrote:
> Forum members - your opinions on the following situation, please:
>
>
>
>  Design standard is 13R 2007 edition.  System type will be antifreeze with a
>  volume exceeding 40 gallon.
>
>
>
>  Per 13R section 6.8.4, "Piping shall be sized using hydraulic calculation
>  procedures in accordance with NFPA 13".   NFPA 13 says to use the
>  Darcy-Weisbach method (section 22.4.4.5.1).
>
>
>
>  Do you think it's the intent of 13R to require the calcs be done using
>  Darcy-Weisbach?
>
>
>
>  Ed Kramer
>
>  Littleton, CO
>