Dewayne,
A short summary of my experience in this situation was the AHJ required
the 3000 square feet if it was a 13 system.
I did use 7psi head pressure to prove a minimum area density of
0.10/3000 vs. the residential head listing pressure required for the
spacing within the 3,000 square feet.
I hope someone else can give you better news.
Kurt Kingston
Commercial Fire Protection Inc.
Mt Vernon, WA 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, April 18, 2008 4:30 AM
To: [email protected]
Subject: NFPA 13 Building with residential heads

NFPA 13 (07ed)
 
I am designing a sprinkler system for a Hotel that falls under NFPA 13.
The floors containing the residential units have a combustible concealed
space
that does not require sprinklers (8.15.1.2.6) but does not qualify for
the 3000 sq ft 
exemption of 11.2.3.1.4 (4)  for unsprinklered combustible concealed
spaces.
If I am using residential sprinklers, are they exempt from this rule
because they are
a specific application sprinkler and not an area/density or room design
method?
Thanks,
Dewayne 