I'll chime in with my opinion.

Does 13 REQUIRE the 3,000 sf DA?  The section that requires the 3,000 sf DA
[11.2.3.1.4(3)] is part of section 11.2 "Occupancy Hazard Fire Control
Approach".  Residential sprinkler design is a separate section (11.3.1) and
is not subject to the requirements of section 11.2.

SHOULD 13 require the 3,000 sf DA?  The underlying premise of 13 is property
protection.  Allowing residential sprinklers to be used in dwelling units
adds to the life safety aspect of the system, but its' still primarily a
property protection system.  For that reason, I can't believe it's the
INTENT of 13 to not require the 3,000 sf DA.  Property protection is
property protection, whether the sprinkler used is a SSP or residential.
That's the exact reason why a .10 gpm/sf density is required when using
residential sprinklers.  So even though I don't think the 3,000 sf DA is
required, I think it should be.

Exit soapbox, stage right.
Ed Kramer
Littleton, CO

 
> NFPA 13 (07ed)
> 
> I am designing a sprinkler system for a Hotel that falls under NFPA 13.
> The floors containing the residential units have a combustible concealed
> space
> that does not require sprinklers (8.15.1.2.6) but does not qualify for
> the 3000 sq ft
> exemption of 11.2.3.1.4 (4)  for unsprinklered combustible concealed
> spaces.
> If I am using residential sprinklers, are they exempt from this rule
> because they are
> a specific application sprinkler and not an area/density or room design
> method?
> Thanks,
> Dewayne