In my opinion, the small room rule can be used.  I believe the 225 sq ft
and 130 sq ft limits are there to restrict the use of special
sprinklers, not to limit the use of other NFPA 13 spacing rules.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: unified facilities criteria question
From: "Tambini, Ed" <[EMAIL PROTECTED]>
Date: Tue, May 13, 2008 5:24 pm
To: <[email protected]>

to all the armed forces people out there:

the UFC 3-600-01 4-2.3.6 lists sprinkler coverage areas to be in
accordance with NFPA 13 except that they must not exceed 225 sq ft for
light hazard areas and 130 sq ft for ordinary hazard. This effectively
rules out extended coverage sprinklers, but does it also rule out the
small room rule for light hazard areas?

thanks,
ed
aero