In my opinion, the small room rule can be used. I believe the 225 sq ft and 130 sq ft limits are there to restrict the use of special sprinklers, not to limit the use of other NFPA 13 spacing rules.
Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell -------- Original Message -------- Subject: unified facilities criteria question From: "Tambini, Ed" <[EMAIL PROTECTED]> Date: Tue, May 13, 2008 5:24 pm To: <[email protected]> to all the armed forces people out there: the UFC 3-600-01 4-2.3.6 lists sprinkler coverage areas to be in accordance with NFPA 13 except that they must not exceed 225 sq ft for light hazard areas and 130 sq ft for ordinary hazard. This effectively rules out extended coverage sprinklers, but does it also rule out the small room rule for light hazard areas? thanks, ed aero _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)