We just finished a layout for NAVFAC PACDIV, for a 2 story dorm. Poured concrete construction, full height concrete walls, floors and roof, every 24'-0" with only 30'-0" front to back.(5200 Sf per floor total) UFC say's you can use 13R, NAVFAC say's NO. UFC say's reduced area for QR heads, NAVFAC say's NO. So we have a two story concrete dorm with a 3000SF design area, 250 GPM hose at the base of riser, and 6" riser and 4" mains, for a job where if we flowed every head between the concrete walls (6) and were overflowing 4 of them, we'd still only need a 3" underground, with 2" mains. Your Tax $$$ at work.
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Vince Sabolik Sent: Tuesday, May 20, 2008 7:47 AM To: [email protected] Subject: RE: unified facilities criteria question Ed -- I wasn't able to use small room at a USMC facility recently, in fact they required a base of 3.000 sf for a wet system. You are however allowed to discount for use of QR heads applied to that 3,000 sf. You can look this up in Table 4-1 in the Unified Facilities Criteria "Fire Protection Engineering for Facilities" Vince At 09:26 AM 5/20/2008, you wrote: >In my opinion, the small room rule can be used. I believe the 225 sq ft >and 130 sq ft limits are there to restrict the use of special >sprinklers, not to limit the use of other NFPA 13 spacing rules. > >Bill Brooks > >William N. Brooks, P.E. >Brooks Fire Protection Engineering Inc. >372 Wilett Drive >Severna Park, MD 21146 >410-544-3620 Phone >410-544-3032 FAX >412-400-6528 Cell > >-------- Original Message -------- >Subject: unified facilities criteria question >From: "Tambini, Ed" <[EMAIL PROTECTED]> >Date: Tue, May 13, 2008 5:24 pm >To: <[email protected]> > >to all the armed forces people out there: > >the UFC 3-600-01 4-2.3.6 lists sprinkler coverage areas to be in >accordance with NFPA 13 except that they must not exceed 225 sq ft for >light hazard areas and 130 sq ft for ordinary hazard. This effectively >rules out extended coverage sprinklers, but does it also rule out the >small room rule for light hazard areas? > >thanks, >ed >aero >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email >to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) Vince Sabolik Christi Fire Protection, Inc. 11351 Pearl Road Strongsville, Ohio 44136 T 440 572-7730 F 440 572-7719 Email: <mailto:[EMAIL PROTECTED]>[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)