Ed --

I wasn't able to use small room at a USMC facility recently, in fact they required a base of 3.000 sf for a wet system. You are however allowed to discount for use
of QR heads applied to that 3,000 sf.

You can look this up in Table 4-1 in the Unified Facilities Criteria "Fire Protection
Engineering for Facilities"


Vince



At 09:26 AM 5/20/2008, you wrote:
In my opinion, the small room rule can be used.  I believe the 225 sq ft
and 130 sq ft limits are there to restrict the use of special
sprinklers, not to limit the use of other NFPA 13 spacing rules.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: unified facilities criteria question
From: "Tambini, Ed" <[EMAIL PROTECTED]>
Date: Tue, May 13, 2008 5:24 pm
To: <[email protected]>

to all the armed forces people out there:

the UFC 3-600-01 4-2.3.6 lists sprinkler coverage areas to be in
accordance with NFPA 13 except that they must not exceed 225 sq ft for
light hazard areas and 130 sq ft for ordinary hazard. This effectively
rules out extended coverage sprinklers, but does it also rule out the
small room rule for light hazard areas?

thanks,
ed
aero
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730 F 440 572-7719 Email: <mailto:[EMAIL PROTECTED]>[EMAIL PROTECTED]