A number of things do not sound right about this situation.  Hopefully
we'll get some references for the NAVFAC case noted earlier.  However,
with respect to the hose flow, I normally take the hose flow at the
nearest hydrant lateral and not at the base of the riser.  For a 13R
system, even with 250 hose added, this is not normally a challenge to
the water supply.

Typically these DoD 13R systems have some 13 areas in the building so
the flows may not be limited to 4 heads inside.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: Re: unified facilities criteria question
From: Gregg Key <[EMAIL PROTECTED]>
Date: Wed, May 21, 2008 9:11 am
To: [email protected]

Which brings up another interesting question. Since UFC 3-600-01
requires a higher hose flow for all of the hazards, does the higher flow
apply to 13R systems? the increased area does not apply due to the
specific requirement of calculating 4 sprinkler heads, but how is the
higher requirement for hose stream accounted for?

Thom McMahon wrote:
> We just finished a layout for NAVFAC PACDIV, for a 2 story dorm. Poured
> concrete construction, full height concrete walls, floors and roof, every
> 24'-0" with only 30'-0" front to back.(5200 Sf per floor total)
> UFC say's you can use 13R, NAVFAC say's NO. UFC say's reduced area for QR
> heads, NAVFAC say's NO. So we have a two story concrete dorm with a 3000SF
> design area, 250 GPM hose at the base of riser, and 6" riser and 4" mains,
> for a job where if we flowed every head between the concrete walls (6) and
> were overflowing 4 of them, we'd still only need a 3" underground, with 2"
> mains. Your Tax $$$ at work.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Vince Sabolik
> Sent: Tuesday, May 20, 2008 7:47 AM
> To: [email protected]
> Subject: RE: unified facilities criteria question
>
> Ed --
>
> I wasn't able to use small room at a USMC facility recently, in fact they
> required
> a base of 3.000 sf for a wet system. You are however allowed to discount
> for use of QR heads applied to that 3,000 sf.
>
> You can look this up in Table 4-1 in the Unified Facilities Criteria "Fire
> Protection Engineering for Facilities"
>
>
>
> Vince
>
>
>
>
> At 09:26 AM 5/20/2008, you wrote:
>> In my opinion, the small room rule can be used. I believe the 225 sq ft
>> and 130 sq ft limits are there to restrict the use of special
>> sprinklers, not to limit the use of other NFPA 13 spacing rules.
>>
>> Bill Brooks
>>
>> William N. Brooks, P.E.
>> Brooks Fire Protection Engineering Inc.
>> 372 Wilett Drive
>> Severna Park, MD 21146
>> 410-544-3620 Phone
>> 410-544-3032 FAX
>> 412-400-6528 Cell
>>
>> -------- Original Message --------
>> Subject: unified facilities criteria question
>> From: "Tambini, Ed" <[EMAIL PROTECTED]>
>> Date: Tue, May 13, 2008 5:24 pm
>> To: <[email protected]>
>>
>> to all the armed forces people out there:
>>
>> the UFC 3-600-01 4-2.3.6 lists sprinkler coverage areas to be in
>> accordance with NFPA 13 except that they must not exceed 225 sq ft for
>> light hazard areas and 130 sq ft for ordinary hazard. This effectively
>> rules out extended coverage sprinklers, but does it also rule out the
>> small room rule for light hazard areas?
>>
>> thanks,
>> ed
>> aero
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>
> Vince Sabolik
> Christi Fire Protection, Inc.
> 11351 Pearl Road
> Strongsville, Ohio 44136
>
> T 440 572-7730 F 440 572-7719 Email:
> <mailto:[EMAIL PROTECTED]>[EMAIL PROTECTED]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to