That's when you have to factor in if what you are doing is going to be o.K.
or not........K?

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
     
 
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew J.
Willis
Sent: Thursday, May 22, 2008 1:44 PM
To: [email protected]
Subject: RE: Its tough getting old

What's a "K" factor??

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Eckard, Mark - Mark E
----- >Sent: Thursday, May 22, 2008 1:29 PM
----- >To: [email protected]
----- >Subject: RE: Its tough getting old
----- >
----- >
----- >The adjusted flow equals the flow of the leg with the 
----- >lowest pressure times the square root of the lowest 
----- >pressure over the higher pressure.
----- >Then add the adjusted flow to the higher flow 
----- >requirement for the total flow required at the higher pressure.
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of George Church
----- >Sent: Thursday, May 22, 2008 1:44 PM
----- >To: [email protected]
----- >Subject: RE: Its tough getting old
----- >
----- >Wow- remember determining the K factors and multiplying 
----- >the lower pressure one by the higher pressure and 
----- >therefore you get the higher flows balanced at the 
----- >higher pressure demand point?
----- >
----- >Move over, cobwebs, trying to recall kRadicalQ.../ glc
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Matthew J.
----- >Willis
----- >Sent: Thursday, May 22, 2008 1:33 PM
----- >To: [email protected]
----- >Subject: RE: Its tough getting old
----- >
----- >You flow them One at the time. Then balance at the point 
----- >they come together.
----- >Then you flow both to ensure they will work together.
----- >
----- >R/
----- >
----- >Matt
----- >
----- >Matthew J. Willis
----- >Living Water Fire Protection, LLC.
----- >1160 McKenzie Rd.
----- >PO Box 877
----- >Cantonment, FL. 32533
----- >850-937-1850 Voice
----- >850-937-1852 Facsimile
----- >[EMAIL PROTECTED]
----- > 
----- >
----- >----- >-----Original Message-----
----- >----- >From: [EMAIL PROTECTED]
----- >----- >[mailto:[EMAIL PROTECTED] On
----- >----- >Behalf Of Dyce Geoffrey H.
----- >----- >Sent: Thursday, May 22, 2008 12:23 PM
----- >----- >To: [email protected]
----- >----- >Cc: Saults Nancy Suzanne
----- >----- >Subject: Its tough getting old
----- >----- >
----- >----- >We have an overhead system and a rack system.  Balancing
----- >----- >the two systems is flowing the two systems at the same
----- >----- >time and your balance point is the point where they both
----- >----- >come together.  Yes??....No???
----- >----- >
----- >----- >Geoffrey H. Dyce
----- >----- >Sales Manager
----- >----- >Contractor I, #87582700012007
----- >----- >NICET IV
----- >----- >Industrial Fire & Safety Inc.
----- >----- >Ph:    727-573-1556
----- >----- >Fx:    727-572-7266
----- >----- >Cell:  727-644-8872
----- >----- >
----- >----- >_______________________________________________
----- >----- >Sprinklerforum mailing list
----- >----- >[email protected]
----- >----- 
----- >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >----- >
----- >----- >To Unsubscribe, send an email
----- >----- >to:[EMAIL PROTECTED]
----- >----- >(Put the word unsubscribe in the subject field)
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to