Gregg,

I was addressing older systems per NFPA 25 built to a prior code where
there is no means to test full-flow and no requirement to add such a
means. Even in these cases you have to forward flow as best you can.

On Fri, May 30, 2008 at 2:13 PM, Gregg Key <[EMAIL PROTECTED]> wrote:
> NFPA 13 2002 ed 8.16.4.6.1  Means SHALL be provided downstream of all
> backflow prevention valves for flow test at system demand.
> 2007 ed 8.17.4.6.1 states the same thing.
>  System acceptance 16.2.5.1 The backflow prevention assembly SHALL be
> forward flow tested to ensure proper operation.
>  A 8.16.4.6.1 gives some ideas how to accomplish this.
>
> Required?  appears so
>
> Thom McMahon wrote:
>>
>> Gentlemen, please remember that 25 only requires the full forward flow if
>> the provisions for it have been made in the riser or system. It does not
>> require that you fail the system, or require the installation of full
>> forward flow appliances it they don't exist. IF they are there use them
>> and
>> test the backflow, if not simply test the backflow as per ASSE or as
>> required by the water AHJ and move on. (It's the same old question with
>> all
>> installations, Did the AHJ allow this at the time, or was this just an
>> installation violation. The assumption is always that the AHJ allowed it,
>> to
>> do otherwise, if the owner says there have been no changes to the system
>> would make inspections a confrontational situation, which would not
>> improve
>> the system reliability.)
>> Thom McMahon, SET
>> Firetech, Inc.
>> 2560 Copper Ridge Dr
>> P.O. Box 882136
>> Steamboat Springs, CO 80488
>> Tel:  970-879-7952
>> Fax: 970-879-7926
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Mark
>> Sornsin
>> Sent: Friday, May 30, 2008 1:45 PM
>> To: [email protected]
>> Subject: RE: Full-flow backflow test
>>
>> That's a good logical argument - but it involves too many steps to be
>> enforced 'round here.  Kind of like a political argument that can't fit on
>> a
>> bumper sticker. So if it's not enforced, the contractors aren't going to
>> add
>> the costs (a criticism of the system, not the contractors).
>>
>> As to section 8.17.4.6.1 ('08 ed): It does not require a test outlet - it
>> requires a means of full-flow testing, which would be satisfied by someone
>> saying that they'll just replace the check valve with a 4 in.
>> elbow and pipe it to the outside on the day of testing...somehow.
>>
>> Mark A. Sornsin, PE
>> Fire Protection Engineer
>> Ulteig Engineers, Inc. Fargo, ND
>> 701.280.8591
>> [EMAIL PROTECTED]
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of David Autry
>> Sent: Friday, May 30, 2008 2:12 PM
>> To: [email protected]
>> Subject: Full-flow backflow test
>>
>> It's required in 25, which is referenced in 13. So that makes it a
>> requirement of 13 (NFPA 13, 2002 edition, 2.1)
>> David Autry
>> Plans Examiner
>> Nebraska State Fire Marshal's Office
>> 246 S. 14th Street
>> Lincoln, NE 68508
>> 402-471-9659
>> 402-471-3118 fax
>> www.sfm.ne.gov
>>  -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Steve
>> Leyton
>> Sent: Friday, May 30, 2008 1:58 PM
>> To: [email protected]
>> Subject: RE: 200 psi test for components rated 175
>>
>> Seeing as the backflow isn't a fire appliance, it makes sense that it's
>> outside the scope of 13.   I'm pretty sure the "full forward flow test"
>> is a jurisdictional agency thing, i.e. NAVFAC or the serving water
>> company.   So fire officials might require it too - for peace of mind
>> perhaps?
>>
>> BTW, you mitigate the clapper issue by turning the FDC body upside down.
>> Duh.
>>
>> Steve Leyton
>> Protection Design & Consulting
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Mark
>> Sornsin
>> Sent: Friday, May 30, 2008 11:33 AM
>> To: [email protected]
>> Subject: RE: 200 psi test for components rated 175
>>
>> Don't most FDCs include clappers?  How do you backwards flow out an FDC
>> with
>> clappers? And what do you do when the system has a high demand volume -
>> say
>> over 500 gpm? You'll have a tough time flowing it out an FDC even without
>> clappers.
>>
>> Seems it's the responsibility of the engineer of record (when they're
>> present) to require the test outlet so the owner has a means of meeting
>> the
>> requirements of NFPA 25 - even if the inspectors never end up testing the
>> backflow.
>>
>> When there is not an engineer of record, and a contractor is asked to
>> design/install a system per code, I don't believe there is any language in
>> NFPA 13 that would force a contractor to install the test outlet.
>>
>> Mark A. Sornsin, PE
>> Fire Protection Engineer
>> Ulteig Engineers, Inc. Fargo, ND
>> 701.280.8591
>> [EMAIL PROTECTED]
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
>> Sent: Friday, May 30, 2008 12:23 PM
>> To: [email protected]
>> Subject: Re: 200 psi test for components rated 175
>>
>> Yep, that could be the reason it is shown.
>>
>> Yea Matt, sorta trick question, We have installed a few wall hydrants at
>> Military bases.
>>        Funny thing is that they do there own inspections and they don't
>> follow NFPA 25 that requires an annual forward flow on the backflows. So
>> the
>> only systems in our area that do have them , are not being used.
>>        OK while we are at it, how many NFPA 25 inspectors perform the
>> required forward flow test annually?
>>
>>
>> -
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to