Don't most FDCs include clappers?  How do you backwards flow out an FDC
with clappers? And what do you do when the system has a high demand
volume - say over 500 gpm? You'll have a tough time flowing it out an
FDC even without clappers.

Seems it's the responsibility of the engineer of record (when they're
present) to require the test outlet so the owner has a means of meeting
the requirements of NFPA 25 - even if the inspectors never end up
testing the backflow.

When there is not an engineer of record, and a contractor is asked to
design/install a system per code, I don't believe there is any language
in NFPA 13 that would force a contractor to install the test outlet.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Friday, May 30, 2008 12:23 PM
To: [email protected]
Subject: Re: 200 psi test for components rated 175

Yep, that could be the reason it is shown.

Yea Matt, sorta trick question, We have installed a few wall hydrants at
Military bases.
        Funny thing is that they do there own inspections and they don't
follow NFPA 25 that requires an annual forward flow on the backflows. So
the only systems in our area that do have them , are not being used.
        OK while we are at it, how many NFPA 25 inspectors perform the
required forward flow test annually?


-
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to