I believe that you are talking about "Obstructed construction" The 22" down has a limit of 1" to 6" below the bottom of the beam, and still remain no more than 22" Max down. See Exhibit 8.15 in 2007.
8.6.4.1.1.3 is in ref to vertical changes in un-obstructed construction. (Handbook has a handy description.)This is to address ceiling pockets and changes in elevation. See exhibit 8-25 and section 8.6.7. Your either obstructed, or un-obstructed. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, July 23, 2008 9:37 AM To: [email protected] Subject: Deflector Distance From Ceiling Forum: I am in need of some clarification and thoughts. Section 8.6.4.1.1 states that sprinkler deflectors for unobstructed construction shall be 1 inch to 12 inches below the ceiling. Section 8.6.4.1.1.3 says the requirements of 8.6.4.1.1 shall not apply for light and ordinary hazard occupancies with ceilings that are non-combustible or limited combustible. I have a concrete ceiling with concrete structural beams that are 18 inches deep and spaced 10 feet on center roughly. By definition, this is unobstructed. Can I place my sprinklers, by code, such that the deflector is more than 12 inches below the ceiling? What is the lowest you can place your deflector if this is the case (we would be no lower than 22 inches, but I am still curious what the limit is)? We can eliminate some sprinklers if we can. If not, the obstruction rules get in the way and we add some sprinklers. Thanks. Andrew Weisfield This email is intended for named recipients only. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - http://www.avg.com Version: 8.0.138 / Virus Database: 270.5.5/1568 - Release Date: 7/23/2008 6:55 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)