That would clarify it.  I was just about to ask if that period should be 
removed.

If that is the case, then this is very specific to ceiling elevation 
changes, not just where there is non-combustible / limited combustible 
ceilings.  Is that the intent?

Thanks.

Andrew Weisfield



"Thom McMahon" <[EMAIL PROTECTED]> 
Sent by: [EMAIL PROTECTED]
07/23/2008 03:51 PM
Please respond to
[email protected]


To
<[email protected]>
cc

Subject
RE: Deflector Distance From Ceiling






8.6.4.1.1.3 From a source close to the committee I've been told that you
remove the period at the end of the sentence, and read it straight 
through,
it's easier to understand, and that it then reflects the committee's 
intent.

Just a little housekeeping for the next edition.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, July 23, 2008 9:37 AM
To: [email protected]
Subject: Deflector Distance From Ceiling

Forum:

I am in need of some clarification and thoughts.  Section 8.6.4.1.1 states 

that sprinkler deflectors for unobstructed construction shall be 1 inch to 

12 inches below the ceiling.  Section 8.6.4.1.1.3 says the requirements of 

8.6.4.1.1 shall not apply for light and ordinary hazard occupancies with 
ceilings that are non-combustible or limited combustible. 

I have a concrete ceiling with concrete structural beams that are 18 
inches deep and spaced 10 feet on center roughly.  By definition, this is 
unobstructed.  Can I place my sprinklers, by code, such that the deflector 

is more than 12 inches below the ceiling?  What is the lowest you can 
place your deflector if this is the case (we would be no lower than 22 
inches, but I am still curious what the limit is)?  We can eliminate some 
sprinklers if we can.  If not, the obstruction rules get in the way and we 

add some sprinklers.

Thanks.

Andrew Weisfield


This email is intended for named recipients only.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.5.5/1568 - Release Date: 7/23/2008
6:55 AM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




This email is intended for named recipients only.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to