I think I have tried the ISO method before and unless I did something
wrong (easily) the fire flows I ended up with for large buildings were
greater than those in Appendix B.

At the very least I will need a lot more information on the existing
building before proposing something other than 6000 gpm to the AHJ.

Thanks to everyone for your input.

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Thursday, July 24, 2008 7:22 AM
To: [email protected]
Subject: RE: Fire Flow Calculation

The reason for the ISO method being more atractive is that ISO allows
the "Effective Area" to be calculated utilizing 2hr fire separations for
compartmentalization.
In simpler words, you are allowed to calculate the fire flow based on
the LARGEST effective area bounded by 2hr construction. This also allows
2hr floor assemblies to be utilized as boundaries as well.

In addition, if your structure is two stories or greater, there is an
allowance for "protected" vertical openings vs. "unprotected" vertical
openings.

The fire protection handbook has a very good section on Needed Fire Flow
and lays out most of the ISO method requirements and allowances.

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Thursday, July 24, 2008 9:32 AM
To: [email protected]
Subject: RE: Fire Flow Calculation

There was an article by Ken Isman from the OFSA (Other Fire Sprinkler
Association) in Sprinkler Quarterly recently (April? A group of people
standing by a fire truck on cover) which ran thru some of the fire flow
calculations, and in it he referenced a previous SQ article from 2003
which had more detail on the subject.

He discusses the difference between the IFC and ISO methods of
determining fire flows, and I recollect the ISO method was more
attractive for reasons I don't recall at this time.

If you have access to SQ, this might be exactly what you're looking for.

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Thursday, July 24, 2008 8:54 AM
To: [email protected]
Subject: RE: Fire Flow Calculation

Ron,

Just a few questions to stimulate the ole thought processes this morning
;-)

(1) What fire flow calculation method are you required (or allowed) to
utilize in the jurisdiction you are referencing?
(2) Have you calculated the "effective area" based on the allowed
compartmentalization of the method you are using? (Such as 2hr fire
separations, 4hr fire separations, etc.)
(3) How is the 200k sqft addition separated from the 150k sqft existing
building?
(4) How is the 50k sqft unsprinklered area separated out of the 150k
sqft existing area?
(5) What reduction in fire flow does you local authority allow for
sprinklers and is there a possibility of an alternate reduction
percentage (ie. 50% instead of 75%) based on the way the 50k sqft area
is separated out of the 150k sqft area?
(6) What was the orginal fire flow requirement for the existing 150k
sqft building and how was the unsprinklered 50k sqft addressed at that
time?

Maybe we can get a better determination of the actual conditions you are
dealing with and a more definitive number than "ALL" or "NONE" in the
fire flow calculation process with a little more information from which
to work.

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com




-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 4:36 PM
To: [email protected]
Subject: Fire Flow Calculation

Looking for help to determine required fire flow. New addition to
hospital is 200k sqft. 150k sqft existing building with 50k sqft of the
150k not sprinklered. Construction type is I-FR.

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

-----------------------------------------------------------------------
    Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into 'The Players Hall of Fame'
       at The Great Games of Business
          http://www.greatgame.com
   Wayne Automatic Fire Spinklers, Inc.
          'Best Places to Work'
       http://tinyurl.com/ov335
      by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

-----------------------------------------------------------------------
    Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into 'The Players Hall of Fame'
       at The Great Games of Business
          http://www.greatgame.com
   Wayne Automatic Fire Spinklers, Inc.
          'Best Places to Work'
       http://tinyurl.com/ov335
      by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to