I have never had an AHJ or Underwriter require an air compressor to be on 
emergency power.  Rationale was that the systems are not supposed be leaking to 
the extent that they should need it for an anticipated short period of power 
loss.  If they are then the systems need to be tested and the leakage fixed.

The 30 minutes was the time once the system is reset and as far as being 
available at all times I was told that was referring to the compressor being 
hard wired into a live circuit, not on a switched circuit that could be turned 
off.

Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reed Roisum
Sent: Thursday, July 24, 2008 1:07 PM
To: '[email protected]'
Subject: Air Compressor Power Supply

A building (nursing home) with an emergency generator has a dry system.  Is the 
air compressor required to be connected to the emergency generator?

NFPA-13 (2007) 7.2.6.2.1,2 says that the air supply shall be from a source 
available at all times and shall be capable of restoring normal air pressure in 
the system within 30 minutes.

Does this imply that yes it would be required to be connected to the em. power 
when available or does it just need to be an unswitched circuit?

It seems as though it would be advisable for the compressor to be on the 
generator circuit but I want to know if it would be required.

Thank you for any input and/or references.

Reed A. Roisum, CET
Fire Protection Technician
NICET Level III

Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079

Direct Number: 701.280.8580
Mobile: 701.212.8810
Main Office: 701.280.8500

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to