But air, argon, or nitrogen, it has to be compressed.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Tuesday, July 29, 2008 11:39 AM
To: Roland Huggins
Subject: Re[2]: Air Compressor Power Supply

Hello Roland,

and to add to that it doesn't even have to be air....

Tuesday, July 29, 2008, 11:14:23 AM, you wrote:

> to continue on this same theme, the air supply is not even REQUIRED to  
> be automatic.  How's that for a kick in the head?

> Roland

> On Jul 28, 2008, at 10:17 AM, John Denhardt wrote:

>> An air compressor is not required by NFPA 13 to be on an emergency or
>> stand-by power.  An air compressor is not required to be listed.  An  
>> air
>> compressor is not even required.
>>
>> I would state normal building power is fine with a disconnect to allow
>> servicing of the air compressor is all that is required.
>>
>> Hope this helps,
>> John

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)


-- 
Best regards,
 Charles Thurston                            mailto:[EMAIL PROTECTED]
  Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to