An air compressor is not required by NFPA 13 to be on an emergency or stand-by power. An air compressor is not required to be listed. An air compressor is not even required.
I would state normal building power is fine with a disconnect to allow servicing of the air compressor is all that is required. Hope this helps, John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reed Roisum Sent: Thursday, July 24, 2008 1:07 PM To: '[email protected]' Subject: Air Compressor Power Supply A building (nursing home) with an emergency generator has a dry system. Is the air compressor required to be connected to the emergency generator? NFPA-13 (2007) 7.2.6.2.1,2 says that the air supply shall be from a source available at all times and shall be capable of restoring normal air pressure in the system within 30 minutes. Does this imply that yes it would be required to be connected to the em. power when available or does it just need to be an unswitched circuit? It seems as though it would be advisable for the compressor to be on the generator circuit but I want to know if it would be required. Thank you for any input and/or references. Reed A. Roisum, CET Fire Protection Technician NICET Level III Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 Direct Number: 701.280.8580 Mobile: 701.212.8810 Main Office: 701.280.8500 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)