to continue on this same theme, the air supply is not even REQUIRED to be automatic. How's that for a kick in the head?

Roland

On Jul 28, 2008, at 10:17 AM, John Denhardt wrote:

An air compressor is not required by NFPA 13 to be on an emergency or
stand-by power. An air compressor is not required to be listed. An air
compressor is not even required.

I would state normal building power is fine with a disconnect to allow
servicing of the air compressor is all that is required.

Hope this helps,
John