Todd, the commentary in section A9.2.1.3 explains the structure only has to
support the actual weight of the sprinkler system.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC
> Sent: Friday, July 25, 2008 12:40 PM
> To: [email protected]
> Subject: beam strength for hangers
> 
> NFPA 13 (2002) 9.1.1.2(1) states that "Hangers shall be designed to
> support five times the weight of water-filled pipe plus 250 lb at
> each point of piping support." Does this mean the hanger assembly
> only, or does make it incumbent on the structural steel to actually
> support this load as well? For a 10 ft piece of 4" sch 10, this would
> equate to a point load of 839 pounds. We have to get some information
> to a CE to figure out how to hang a system.
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080