Never saw that one before. Thanks
At 03:06 PM 7/25/2008, you wrote:
Todd,
see 9.2.1.3 (07) under building structure. Not sure which parag, in 02
R/
Matt
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, July 25, 2008 1:40 PM
To: [email protected]
Subject: beam strength for hangers
NFPA 13 (2002) 9.1.1.2(1) states that "Hangers shall be designed to
support five times the weight of water-filled pipe plus 250 lb at each
point of piping support." Does this mean the hanger assembly only, or
does make it incumbent on the structural steel to actually support this
load as well? For a 10 ft piece of 4" sch 10, this would equate to a
point load of 839 pounds. We have to get some information to a CE to
figure out how to hang a system.
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)