>But that didn't answer your question. In my opinion NFPA-13 only applies to the hanger assembly itself. Does that mean the sprinkler designer is off the hook ?. By no means >someone has to do the load calculation otherwise the application is incomplete.
Exactly. The paragraph I mentioned (9.2.1.3) pertaining to the Building Structure in 13 has been used to make the sprinkler contractor hire a structural engineering firm to provide proof that we were in compliance with Chap 9 of Our standard. In Todd's situation.. the hanger has to meet 5 times plus 250. Since it is not listed under the section for Building Structure in 13, the 5 times does not need to be added, only the weight plus 250. R/ Matt _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)