Ed:

This system is entirely in the attic.  The riser is the only portion that is
in the heated space.

I do these calculations in 2 parts.  I calculate the system back to the
interface of anti-freeze solution / water and get a pressure & flow demand
at that point utilizing the DW calcs.  I then do a second calculation using
HW that is from the city supply to the interface point.  

It is basically how we used to do rack systems calculations.  You calc the
rack system and get a k-factor with pressure/flow demands.  Plug that into
the overhead system and there you go.

In several people that I have talked to today about this, I am getting about
50/50 of saying to use each temp.  It is pretty funny.  I am still waiting
on the AHJ.  Hopefully, I can get a pretty decent concensus soon.  

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Thursday, September 18, 2008 2:43 PM
To: [email protected]
Subject: RE: viscosities

Travis,

This doesn’t address your question, but I'm curious if the entire AF system
is subject to outdoor temps (or just part of it).

I ask, because if a significant part of the system is in a heated area, then
it further complicates selecting an appropriate viscosity.  My limited
understanding of HydraCalc is that a single viscosity and a single density
is entered for the entire calc (if I'm wrong, someone please correct me).
Do you use the high viscosity (extreme min temp), the medium viscosity
(average min temp) or the low viscosity (room temp)?  Obviously the room
temp viscosity wouldn't be appropriate, but how's a designer to choose?  As
in your example, the selected viscosity can make a whale of a difference in
system costs.

I've yet to calc an AF system using Darcy-Weisbach, so I'm hoping someone
can enlighten me.

Ed Kramer
Littleton, CO



> Ok..another viscosity question.
> 
> When using HydraCalc to calculate antifreeze systems using the Darcy 
> method, it asks for viscosities of solutions.  I have a data sheet 
> with the viscosities at various concentrations and various 
> temperatures.  My question is, do you use the average daily minimum 
> temperature for an area, or the extreme daily minimum for an area?  
> For this particular project, the difference is 40°F in the 2 
> temperatures.  With the average daily minimum temperature, the system
works with the available pressure.
> With the extreme daily minimum, the city supply is not even close.
> There is a 100+ psi swing in the demands.
> 
> So, do we go with average minimums, or extreme minimums?
> 
> There is always the option to go to a dry system, but the increased 
> design areas and reduced c factor will also force a pump on this 
> project.  An anti-freeze system at average daily minimum works without 
> a fire pump.
> However, we don't want to design/install an inadequate system.
> 
> 
> Please feel free to call if you have any questions or comments.
> 
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Dr
> Gilbert, AZ 85298
> 480-505-9271
> [EMAIL PROTECTED]
> 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 3453 (20080918) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to