Ed:

Yeah, we were able to make the system work at viscosities for 0F.  According
to one of the gov't websites, the temperature was only below 0 for 20 days
in something like the last 20 years.  So, it was deemed reasonable to go
with the viscosities for 0F.  I believe it works out to about 99.8% of the
time, the temps will be above 0F.  If the global warming boys are right,
then it may be even less :-)

I would love to see more guidance for the temperatures to be used for the DW
calcs.  It can make huge swings in the requirements.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Friday, September 19, 2008 10:11 AM
To: [email protected]
Subject: RE: viscosities

Thanks, Travis.  Seems more complicated than it has to be, but I guess
that’s how you get around software limitations.

Concerning your original question:  I noticed on a different forum you & the
AHJ agreed to use a temp that is subceeded (if that’s a word) only about
once per year.  Seems reasonable.  


Roland:  It wouldn't hurt my feelings if the DW requirement was tossed.
Barring that, there certainly should be more guidance for temperature
selection.  I envision a lot of layout techs (myself included) fumbling big
time.  Getting input from the AHJ is a great idea, but they also need
guidance.  

Using Travis' project as an example, how's a contractor supposed to bid
something like that?

Ed Kramer
Littleton, CO




> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum- 
> [EMAIL PROTECTED] On Behalf Of Travis Mack, SET
> Sent: Thursday, September 18, 2008 4:10 PM
> To: [email protected]
> Subject: RE: viscosities
> 
> Ed:
> 
> This system is entirely in the attic.  The riser is the only portion 
> that is in the heated space.
> 
> I do these calculations in 2 parts.  I calculate the system back to 
> the interface of anti-freeze solution / water and get a pressure & 
> flow demand at that point utilizing the DW calcs.  I then do a second 
> calculation using HW that is from the city supply to the interface 
> point.
> 
> It is basically how we used to do rack systems calculations.  You calc 
> the rack system and get a k-factor with pressure/flow demands.  Plug 
> that into the overhead system and there you go.
> 
> In several people that I have talked to today about this, I am getting 
> about 50/50 of saying to use each temp.  It is pretty funny.  I am 
> still waiting on the AHJ.  Hopefully, I can get a pretty decent 
> concensus soon.
> 
> 
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ed 
> Kramer
> Sent: Thursday, September 18, 2008 2:43 PM
> To: [email protected]
> Subject: RE: viscosities
> 
> Travis,
> 
> This doesn’t address your question, but I'm curious if the entire AF 
> system is subject to outdoor temps (or just part of it).
> 
> I ask, because if a significant part of the system is in a heated 
> area, then it further complicates selecting an appropriate viscosity.  
> My limited understanding of HydraCalc is that a single viscosity and a 
> single density is entered for the entire calc (if I'm wrong, someone 
> please correct me).
> Do you use the high viscosity (extreme min temp), the medium viscosity 
> (average min temp) or the low viscosity (room temp)?  Obviously the 
> room temp viscosity wouldn't be appropriate, but how's a designer to
choose?
> As
> in your example, the selected viscosity can make a whale of a 
> difference in system costs.
> 
> I've yet to calc an AF system using Darcy-Weisbach, so I'm hoping 
> someone can enlighten me.
> 
> Ed Kramer
> Littleton, CO
> 
> 
> 
> > Ok..another viscosity question.
> >
> > When using HydraCalc to calculate antifreeze systems using the Darcy 
> > method, it asks for viscosities of solutions.  I have a data sheet 
> > with the viscosities at various concentrations and various 
> > temperatures.  My question is, do you use the average daily minimum 
> > temperature for an area, or the extreme daily minimum for an area?
> > For this particular project, the difference is 40°F in the 2 
> > temperatures.  With the average daily minimum temperature, the 
> > system
> works with the available pressure.
> > With the extreme daily minimum, the city supply is not even close.
> > There is a 100+ psi swing in the demands.
> >
> > So, do we go with average minimums, or extreme minimums?
> >
> > There is always the option to go to a dry system, but the increased 
> > design areas and reduced c factor will also force a pump on this 
> > project.  An anti-freeze system at average daily minimum works 
> > without a fire pump.
> > However, we don't want to design/install an inadequate system.
> >
> >
> > Please feel free to call if you have any questions or comments.
> >
> > Travis Mack, SET
> > MFP Design, LLC
> > 2508 E Lodgepole Dr
> > Gilbert, AZ 85298
> > 480-505-9271
> > [EMAIL PROTECTED]
> >
> 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
> 
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
> field)
> 
> __________ NOD32 3453 (20080918) Information __________
> 
> This message was checked by NOD32 antivirus system.
> http://www.eset.com
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
> 
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
> field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 3456 (20080919) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to