Keith, Steve

Take a look at 2006 IBC 905.3; "Standpipe systems are allowed to be combined
with automatic sprinkler systems"

Does that help you're situation ?

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Friday, October 31, 2008 4:00 PM
To: [email protected]; [email protected]
Subject: RE: Standpipe system

The building code described specific conditions where hose valves can be
connected to sprinkler systems, such as covered mall buildings.   NFPA 14
describes the requirements for design of standpipe systems; NFPA 13 same for
sprinkler systems.   Both standards prescribe the provisions for combined
systems but IF you're requirement is for a standpipe system (as prescribed
by CODE), then the answer is likely that the hose connections can't just be
taken off the sprinkler piping.    Unfortunately, it's not just a yes/no
equation so the answer is conditional.
 
Steve Leyton
Protection Design & Consulting

________________________________

From: [EMAIL PROTECTED] on behalf of Keith Pepin
Sent: Fri 10/31/2008 8:26 AM
To: [email protected]
Subject: Standpipe system



The Engineer of Record has indicated that standpipe hose valves shall be
located in a building that we are designing. Of course he hasn't shown how
they are to be connected, his note is to connect to the sprinkler system. In
the past I have ran a separate main w/ a control valve from the riser to
feed the hose valves. Can they be connected to the sprinkler mains?



Thanks

Keith





_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to