Forgot to point out that it is a combined standpipe serving the sprinklers also, so either you run the standpipe at the intermediate landing location and pipe up to the sprinkler OR run the standpipe at the floor level location and pipe up or down to a hose valve.
David Autry Plans Examiner Nebraska State Fire Marshal's Office 246 S. 14th Street Lincoln, NE 68508 402-471-9659 402-471-3118 fax www.sfm.ne.gov ** Note new email address: [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, November 12, 2008 3:58 PM To: [email protected] Subject: RE: NFPA 14 One of the other reasons they are installed at the intermediate instead of the exit landings is space. At the exit landing you are generally coming out of a door and depending on where the riser is in relation to the door, it can encroach into the egress path. When the valve is on the intermediate level the path of traffic is usually closer to the center of the stair than at the outer edges coming around the corner at the landing. Unless there are some physical restrictions it shouldn't be any harder to install the valves at the intermediate landing than the exit landing. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Autry, David Sent: Wednesday, November 12, 2008 4:44 PM To: [email protected] Subject: NFPA 14 Speaking of Standpipes, NFPA 14 (2003, Edition) 7.3.2 (1) Class I standpipe systems shall be provided with 2 1/2" hose connections at each intermediate landing between floor levels in every required exit stairway. What are the ramifications of allowing the hose connections to be on the floor landings? I realize the benefits to firefighters of the valve being between floors. The contractor submitted plans and I pointed out the code requires them to be at the intermediate landings. "Well that's where they're shown on the Mech. Plans." I ASSUME they were shown there by a PE of one discipline or another and were missed during the architectural review. It just seems to me to be a royal pain in the a** to install these valves at the intermediate landings. Any thoughts from the mighty Forum? David Autry Plans Examiner Nebraska State Fire Marshal's Office 246 S. 14th Street Lincoln, NE 68508 402-471-9659 402-471-3118 fax www.sfm.ne.gov ** Note new email address: [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, November 12, 2008 2:42 PM To: [email protected] Subject: Re: design and coordination roles and responsibilities. My favorite story in the ongoing battle between the professionals is the difficulty Steve Leyton had with a registered PE who informed him that by the virtue of his lack of registration as a PE that he was "unqualified" to discuss the issues related to standpipe design, use, and compliance with NFPA-14. The fact that Steve was a member of the NFPA-14 committee at the time escaped the notice of the individual, and in a delicious moment of irony Steve pointed to his name in the front of the book. That was a day I'll long cherish. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website Ron Greenman wrote: > Once I was called incompetent by the architect because in the field > there was one inch of clear space between the bottom of the beams in a > parking garage and the minimum low clearance for the cars and I > couldn't fit a four inch pipe in the space (and I couldn't touch the > beams. He drew nine inches but the excavator screwed up, the garage > got poured and it was my problem somehow. > > On Wed, Nov 12, 2008 at 11:39 AM, Thom McMahon <[EMAIL PROTECTED]> wrote: > >> Your RIGHT! Because the sprinkler contractor is now the only one that >> does his layout in 3D he visualizes all of the problems the others >> call "Field Conditions". >> Architects get really pissed off when you point out that they and >> their consultants didn't co-ordinate space above the ceiling even >> with their own structural engineer. Yeah the ceiling to bottom of >> floor is 36", and there are recessed lights in the ceiling with >> lenses that make them 8" deep. And yes you clearly show the 16x30 >> duct, and the cable tray and our main is only 6", so what's your >> problem? COULD IT POSSABLY BE THAT W30 beam we're all shown crossing? >> >> Since ancient times the builder of empires and Architects have had >> the same theory, KILL the messenger!! >> >> Thom McMahon, SET >> Firetech, Inc. >> 2560 Copper Ridge Dr >> P.O. Box 882136 >> Steamboat Springs, CO 80488 >> Tel: 970-879-7952 >> Fax: 970-879-7926 >> >> >> -----Original Message----- >> From: [EMAIL PROTECTED] >> [mailto:[EMAIL PROTECTED] On Behalf Of Todd >> Williams >> - FPDC >> Sent: Wednesday, November 12, 2008 10:59 AM >> To: [email protected] >> Subject: RE: design and coordination roles and responsibilities. >> >> One of the consistent problems we have up here is the electrician. >> They don't take part in the coordination process, they often don't >> even have CAD drawings and they just run everything where they want. >> And the GC's tend to let them get away with a lot of it. I find that >> more problems with the architect's concepts surface in the sprinkler >> design that any of the other trades. >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> For Technical Assistance, send an email to: >> [EMAIL PROTECTED] >> >> To Unsubscribe, send an email >> to:[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) >> >> > > > > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)