Speaking of Standpipes, NFPA 14 (2003, Edition) 7.3.2 (1) Class I standpipe systems shall be provided with 2 1/2" hose connections at each intermediate landing between floor levels in every required exit stairway.
What are the ramifications of allowing the hose connections to be on the floor landings? I realize the benefits to firefighters of the valve being between floors. The contractor submitted plans and I pointed out the code requires them to be at the intermediate landings. "Well that's where they're shown on the Mech. Plans." I ASSUME they were shown there by a PE of one discipline or another and were missed during the architectural review. It just seems to me to be a royal pain in the a** to install these valves at the intermediate landings. Any thoughts from the mighty Forum? David Autry Plans Examiner Nebraska State Fire Marshal's Office 246 S. 14th Street Lincoln, NE 68508 402-471-9659 402-471-3118 fax www.sfm.ne.gov ** Note new email address: [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, November 12, 2008 2:42 PM To: [email protected] Subject: Re: design and coordination roles and responsibilities. My favorite story in the ongoing battle between the professionals is the difficulty Steve Leyton had with a registered PE who informed him that by the virtue of his lack of registration as a PE that he was "unqualified" to discuss the issues related to standpipe design, use, and compliance with NFPA-14. The fact that Steve was a member of the NFPA-14 committee at the time escaped the notice of the individual, and in a delicious moment of irony Steve pointed to his name in the front of the book. That was a day I'll long cherish. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website Ron Greenman wrote: > Once I was called incompetent by the architect because in the field > there was one inch of clear space between the bottom of the beams in a > parking garage and the minimum low clearance for the cars and I > couldn't fit a four inch pipe in the space (and I couldn't touch the > beams. He drew nine inches but the excavator screwed up, the garage > got poured and it was my problem somehow. > > On Wed, Nov 12, 2008 at 11:39 AM, Thom McMahon <[EMAIL PROTECTED]> wrote: > >> Your RIGHT! Because the sprinkler contractor is now the only one that does >> his layout in 3D he visualizes all of the problems the others call "Field >> Conditions". >> Architects get really pissed off when you point out that they and their >> consultants didn't co-ordinate space above the ceiling even with their own >> structural engineer. Yeah the ceiling to bottom of floor is 36", and there >> are recessed lights in the ceiling with lenses that make them 8" deep. And >> yes you clearly show the 16x30 duct, and the cable tray and our main is only >> 6", so what's your problem? COULD IT POSSABLY BE THAT W30 beam we're all >> shown crossing? >> >> Since ancient times the builder of empires and Architects have had the same >> theory, KILL the messenger!! >> >> Thom McMahon, SET >> Firetech, Inc. >> 2560 Copper Ridge Dr >> P.O. Box 882136 >> Steamboat Springs, CO 80488 >> Tel: 970-879-7952 >> Fax: 970-879-7926 >> >> >> -----Original Message----- >> From: [EMAIL PROTECTED] >> [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams >> - FPDC >> Sent: Wednesday, November 12, 2008 10:59 AM >> To: [email protected] >> Subject: RE: design and coordination roles and responsibilities. >> >> One of the consistent problems we have up here is the electrician. >> They don't take part in the coordination process, they often don't even have >> CAD drawings and they just run everything where they want. >> And the GC's tend to let them get away with a lot of it. I find that more >> problems with the architect's concepts surface in the sprinkler design that >> any of the other trades. >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> For Technical Assistance, send an email to: [EMAIL PROTECTED] >> >> To Unsubscribe, send an email to:[EMAIL PROTECTED] >> (Put the word unsubscribe in the subject field) >> >> > > > > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)