Speaking of Standpipes,
NFPA 14 (2003, Edition) 7.3.2 (1)
Class I standpipe systems shall be provided with 2 1/2" hose connections at 
each intermediate landing between floor levels in every required exit stairway.

What are the ramifications of allowing the hose connections to be on the floor 
landings?

I realize the benefits to firefighters of the valve being between floors.

The contractor submitted plans and I pointed out the code requires them to be 
at the intermediate landings. "Well that's where they're shown on the Mech. 
Plans." I ASSUME they were shown there by a PE of one discipline or another and 
were missed during the architectural review.

It just seems to me to be a royal pain in the a** to install these valves at 
the intermediate landings.

Any thoughts from the mighty Forum?


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, November 12, 2008 2:42 PM
To: [email protected]
Subject: Re: design and coordination roles and responsibilities.

My favorite story in the ongoing battle between the professionals is the
difficulty Steve Leyton had with a registered PE who informed him that
by the virtue of his lack of registration as a PE that he was
"unqualified" to discuss the issues related to standpipe design, use,
and compliance with NFPA-14.  The fact that Steve was a member of the
NFPA-14 committee at the time escaped the notice of the individual, and
in a delicious moment of irony Steve pointed to his name in the front of
the book.

That was a day I'll long cherish.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



Ron Greenman wrote:
> Once I was called incompetent by the architect because in the field
> there was one inch of clear space between the bottom of the beams in a
> parking garage and the minimum low clearance for the cars and I
> couldn't fit a four inch pipe in the space (and I couldn't touch the
> beams. He drew nine inches but the excavator screwed up, the garage
> got poured and it was my problem somehow.
>
> On Wed, Nov 12, 2008 at 11:39 AM, Thom McMahon <[EMAIL PROTECTED]> wrote:
>
>> Your RIGHT! Because the sprinkler contractor is now the only one that does
>> his layout in 3D he visualizes all of the problems the others call "Field
>> Conditions".
>> Architects get really pissed off when you point out that they and their
>> consultants didn't co-ordinate space above the ceiling even with their own
>> structural engineer. Yeah the ceiling to bottom of floor is 36", and there
>> are recessed lights in the ceiling with lenses that make them 8" deep. And
>> yes you clearly show the 16x30 duct, and the cable tray and our main is only
>> 6", so what's your problem? COULD IT POSSABLY BE THAT W30 beam we're all
>> shown crossing?
>>
>> Since ancient times the builder of empires and Architects have had the same
>> theory, KILL the messenger!!
>>
>> Thom McMahon, SET
>> Firetech, Inc.
>> 2560 Copper Ridge Dr
>> P.O. Box 882136
>> Steamboat Springs, CO 80488
>> Tel:  970-879-7952
>> Fax: 970-879-7926
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
>> - FPDC
>> Sent: Wednesday, November 12, 2008 10:59 AM
>> To: [email protected]
>> Subject: RE: design and coordination roles and responsibilities.
>>
>> One of the consistent problems we have up here is the electrician.
>> They don't take part in the coordination process, they often don't even have
>> CAD drawings and they just run everything where they want.
>> And the GC's tend to let them get away with a lot of it. I find that more
>> problems with the architect's concepts surface in the sprinkler design that
>> any of the other trades.
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>>
>> To Unsubscribe, send an email to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>
>
>
>
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to