What spec or drawings did you bid to?

If design-build I don't see what the problem is. 

If he spec'ed "traditional coverage over the increased area" or fancy words
to that effect you probably have a problem unless you identified the
deviation in the bidding process. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dennis
Browning
Sent: Thursday, November 13, 2008 11:10 AM
To: [email protected]
Subject: Slippery Slope

I have a project we designed the Dry System with  7 SD Attic heads. The ME
wants the Area and Slope increases per 11.2.3.2.4 and 11.2.3.2.5. I pointed
out the listing of the Attic heads but all he says is " If it's OK with the
Local AHJ, he takes " no exception to that design approach" but he will not
stamp the drawings saying this, even tho he DID stamp the first set "
rejected/ resubmit"! 

LOcal AHJ requires plans to be stamped by the EOR or the Architect prior to
submission, and the Architect won't stamp them " because".

Trying to build a case that what we did is " per NFPA 13 and industry
standard. 
Any thoughts?
Dennis Browning
Browning Fire
Medford, Oregon
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to