The FDC has to be installed downstream of the backflow
At 03:48 PM 11/13/2008, you wrote:
Forum,
I have a situation where the fire department is requiring a post
indicator valve and free standing FDC outside the building. We will
also need a backflow preventer installed inside in the sprinkler
control room. Is it permissible to install the FDC so it ties into
the fire line prior to the backflow control valves, or would we need
to install a separate FDC line into the building?
I know 8.16.1.1.1.3 does not allow a shutoff valve in the line, but
it seems contradictory with Figure A.8.16.1.1 2007 NFPA 13.
Thanks,
Jamie Seidl